I need to put in 4 sockets in a shop, where the sockets are going is a 6mm radial from an old circuit, its on a 32a rcbo, can i pull this 6mm into a 4 pole isolator and run a ring out of it, iv looked through the regs and cant really find anything thats says i cant.

[ElectriciansForums.net] Radial to Ring
 
what you are describing is a so called lollipop ring, these are not prevented by the regulations but can be a nightmare to identify later.

A radial circuit can have as many outlets as you need so long as you are not overloading the cable. A 6mm2 cable with a 32A breaker is perfectly fine for plenty of socket outlets.
You would just find it a bit tight to get 2 6mm2 in one SO. But you could also drop the csa to 4mm and continue as a standard 32A 4mm radial.

(it is an unfused spur off a ring that can only be one outlet)
 
6mm s gonny be a tight fit check new sockets as some manufacturers are better than others for accomodating there is one on the market has 2 terminals at each connection but i cant mind the make for the life of me CLIK comes to mind tho
 
what you are describing is a so called lollipop ring, these are not prevented by the regulations but can be a nightmare to identify later.

So is this what used to be done? 4mm to jb then Ring from there?
I was always under the impression that this was frowned upon?
Generally, yes frowned upon but not dangerous or against the regs, just inconvenient to test and check later. I do not think it was ever standard, (but I could be wrong)
 
I have seen lots of them in a university science department. They ran a 6mm to the labs, and then had a DP isolator. This then fed the ring. RCD protection was added in some labs, but not in others, due to experiments that could be ruined if the power was lost.
 
A lot of council and miners mansion housing back in the 60's was wired similar to this.

You would have a ring running around, and at every socket point the ring would go into a JB and then a single cable out to the socket, it was felt you used less cable which I suppose you did, easier chasing in a single cable rather than 2 cables and easier connecting into a socket.

Always threw me at first, but got use to it
 

Reply to Radial to Ring in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
328
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
762
  • Question
Why aren't you asking them?
Replies
5
Views
860

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top