if we have a standard lamp where the flex could be damaged, then that flex must be able to take the rating of the plug, so even a 60W lamp needs a 1.5 mm sq flex,

It's a fixed load so it only needs to be large enough to meet the adiabatic requirements to clear a short-circuit. 0.75mm² is sufficient for 16A OCPD, hence this is the standard minimum cable size for portable appliances in Europe.

I so often find them working but dangerous.

Dangerous, or non-compliant? I have in the past offered a reward for anyone who can provide evidence that a broken 32A RFC has caused actual danger or measurable deterioration specifically due to overloading of cables after losing continuity. Still waiting...
 
Considering a single 2.5 conductor has a larger csa than that of a 30A semi-enclosed fuse element it is going to require some adverse installation method and considerable loading before deterioration occurs.
 
I have in the past offered a reward for anyone who can provide evidence that a broken 32A RFC has caused actual danger or measurable deterioration specifically due to overloading of cables after losing continuity. Still waiting..
When I was redoing our server room at last job, I stripped out redundant cabling. Before I started, I'd measured the load in what I assumed to be an RFC - about 30A, steady, 24 hours a day. It was only when I got to disconnecting stuff that I found it was two radials off one B32. One fed the alarm so little load. The other had started as a radial with two FCUs, but had been extended by a professional and supposedly qualified electrician with another two FCUs. So 30A through a single 2.5 t&e in mini trunking.
Yes, it ran noticably warm to the touch, but the cable didn't seem any worse for it.
 
When I was redoing our server room at last job, I stripped out redundant cabling. Before I started, I'd measured the load in what I assumed to be an RFC - about 30A, steady, 24 hours a day. It was only when I got to disconnecting stuff that I found it was two radials off one B32. One fed the alarm so little load. The other had started as a radial with two FCUs, but had been extended by a professional and supposedly qualified electrician with another two FCUs. So 30A through a single 2.5 t&e in mini trunking.
Yes, it ran noticably warm to the touch, but the cable didn't seem any worse for it.
I’ve come across a number of properties with the same problem appears as though they are on RFC when I’m actual fact they are just 2 radials done my head in when I was doing continuity at board and then hunting down the apparent break in ring to find there was no break in ring but 2 radials. No issue with wiring though no scorch marks or anything but non compliant and solved by converting into 2 x radials.
 
Welcome to the forum mate.
So in a typical 3 bedroom house in France, how many circuits are you looking at if it's all radial?

Your location says 'Surrey' but your flag is France. That's why I put France in my post.

Typical rural French three phase three bedroom house consumer unit.
 

Attachments

  • [ElectriciansForums.net] Radials V Ring mains
    DSC01893.jpeg
    75.6 KB · Views: 24
I certainly do I think it's wonderful and does show that in France multiple RCD's and RCBO's are the norm as is domestic three phase.

It's also gratifying to know that you follow my posts so closely. ?
 
Last edited:
Radials are getting more popular now, especially in flats etc, you all probably no this already, as long as the 2.5mm radial servs no more than 50 Mt's2 protected by 20amp, no problems easy for testing.
 

Reply to Radials V Ring mains in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
373
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
939
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Joining the ends of the radials together to form a ring, and changing the circuit protection to a single 32A would solve the MCB overload problem...
Replies
8
Views
776
https://www.amazon.co.uk/gp/product/B08CJ3VC79/ref=ppx_yo_dt_b_asin_title_o05_s00?ie=UTF8&psc=1 I use this, current clamps go round each outgoing...
Replies
3
Views
725

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top