Hello Guys

Looking for some advice with regards to a extension job. Customer has ordered a Rangemaster Induction Hob and Oven.

I've looked at the specification and it states that potential full load is 14.8Kw. My initial plan was to run a 10mm Twin and Earth but I'm wondering if it would potentially need a 16mm. I understand diversity applies to cooker circuits and its full load will likely not be ever used but was looking for a bit of advice. Would 16mm supply cable be over kill.


Thanks
 
Diversity will apply. Have a read of the chapter in the OSG on max demand and diversity. From that, you should be able to calculate a design current for the circuit, and from there be able to design your circuit. Also have a look at manufacturer's instructions regarding maximum conductor sizes, suggested protective device etc.
 
Diversity will apply. Have a read of the chapter in the OSG on max demand and diversity. From that, you should be able to calculate a design current for the circuit, and from there be able to design your circuit. Also have a look at manufacturer's instructions regarding maximum conductor sizes, suggested protective device etc.
I've just checked the manufacturers installation booklet again
Diversity will apply. Have a read of the chapter in the OSG on max demand and diversity. From that, you should be able to calculate a design current for the circuit, and from there be able to design your circuit. Also have a look at manufacturer's instructions regarding maximum conductor sizes, suggested protective device etc.
I've just checked the manufacturers Instruction and it states a 45Amp Fuse Rating. Nothing about size of conductor but a 10mm should be suffice on a 50amp RCBO.

Cheers for the pointer👍
 
I've just checked the manufacturers installation booklet again

I've just checked the manufacturers Instruction and it states a 45Amp Fuse Rating. Nothing about size of conductor but a 10mm should be suffice on a 50amp RCBO.

Cheers for the pointer👍
Done a quick calculation as per Page 122 of OSG and it should pull in 27 Amps with Diversity applied.
 

Reply to Rangemaster Cooker Load in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
503
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
975
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
907

Similar threads

  • Question
When you say plus kettle, does this indicate you are needing 13A socket/s on the island and a hob supply? and then an oven supply on a tall...
Replies
5
Views
784
I generally thought double stack boards were more for situations where a portrait design is better suited to the cupboard - you still generally...
Replies
4
Views
460

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top