Rather High Ze with all the bonding in place | on ElectriciansForums
Discuss Rather High Ze with all the bonding in place in the UK Electrical Forum area at ElectriciansForums.net
london
Carrying out an EICR on a property in london, the supply is a TN-S supply with an incorrect tenby earth clamped around the PILC Sub mains cable.
Long lead tested all the main bonds and i am very surprised to still get such a high reading with these parallel paths in place.
3.25ohms
With the bonding disconnected 3.25 which remains relatively the same with the bonding connected again
Would i be correct in saying the DNO will need to be notified and called out?
Sounds like the DNO lead sheath is not providing a good earth path, and if the readings stay the same regardless of protective bonding connected or not, then the gas/water supply pipes are probably plastic and therefore not providing any earth.
Contact the DNO to sort their cable
Was the main Earth dissed from the CU when you tested Ze why mess with the Main bonding? after all you are testing the earth fault impedance with the main earth dissed. aren't you?
Yes he is testing 3 Phase but the principle is the same for SP&N
Yes but let's assume the Ze is/was 3.25 Ohms fine, however whether I connect the bonding or not this will make not a jot of difference. It is somewhat confusing the description of the scenario. In any event if the external impedance is that high, then yes of course the DNO must rectify it. However they could say there is no earth someone put that BS953 clamp on and it's nothing to do with us we only have to maintain an earth we supply. In which case it's tough TT for you.
Reply to Rather High Ze with all the bonding in place in the UK Electrical Forum area at ElectriciansForums.net
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...