Location
london
Carrying out an EICR on a property in london, the supply is a TN-S supply with an incorrect tenby earth clamped around the PILC Sub mains cable.
Long lead tested all the main bonds and i am very surprised to still get such a high reading with these parallel paths in place.
3.25ohms
With the bonding disconnected 3.25 which remains relatively the same with the bonding connected again

Would i be correct in saying the DNO will need to be notified and called out?
 
Last edited:
Carrying out an EICR on a property in london, the supply is a TN-S supply with an incorrect tenby earth clamped around the PILC Sub mains cable.
Long lead tested all the main bonds and i am very surprised to still get such a high reading with these parallel paths in place.

Would i be correct in saying the DNO will need to be notified and called out
?????????????????????????????????
 
Sounds like the DNO lead sheath is not providing a good earth path, and if the readings stay the same regardless of protective bonding connected or not, then the gas/water supply pipes are probably plastic and therefore not providing any earth.
Contact the DNO to sort their cable
 
Was the main Earth dissed from the CU when you tested Ze why mess with the Main bonding? after all you are testing the earth fault impedance with the main earth dissed. aren't you?
Yes he is testing 3 Phase but the principle is the same for SP&N
 
Yes but let's assume the Ze is/was 3.25 Ohms fine, however whether I connect the bonding or not this will make not a jot of difference. It is somewhat confusing the description of the scenario. In any event if the external impedance is that high, then yes of course the DNO must rectify it. However they could say there is no earth someone put that BS953 clamp on and it's nothing to do with us we only have to maintain an earth we supply. In which case it's tough TT for you.
 

Reply to Rather High Ze with all the bonding in place in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
438
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
963

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top