Rather High Ze with all the bonding in place | Page 2 | on ElectriciansForums

Discuss Rather High Ze with all the bonding in place in the UK Electrical Forum area at ElectriciansForums.net

Joined
Dec 24, 2016
Messages
404
Reaction score
92
Location
london
Carrying out an EICR on a property in london, the supply is a TN-S supply with an incorrect tenby earth clamped around the PILC Sub mains cable.
Long lead tested all the main bonds and i am very surprised to still get such a high reading with these parallel paths in place.
3.25ohms
With the bonding disconnected 3.25 which remains relatively the same with the bonding connected again

Would i be correct in saying the DNO will need to be notified and called out?
 
Last edited:
I don't see that eradicating parallel paths just disconnecting the bonding to services. If the main earth is connected to the earth bus-bar in the DB then it is connected to all the earths for each final circuit which in turn will connect for instance through the boiler earth to water and or gas. Or the Electric shower through the earth on that to water again to earth and so on. The only way I can see to definitely remove the chance of parallel paths is to disconnect the main earth from the DB bus-bar. Please tell me if I am wrong, although I hardly need say that!
 
Ideally ALL installations should have some thing like this....
[ElectriciansForums.net] Rather High Ze with all the bonding in place

....to make testing easier.
 
It’s not particularly difficult to disconnect the earthing conductor in a domestic installation unless you have say 3 x 10mm conductors not identifying their function and not obvious to o what they supply/connect to, as is often the case in older installations where the tails are 16mm and the earthing conductor is 10mm.
 
Sounds like the DNO lead sheath is not providing a good earth path, and if the readings stay the same regardless of protective bonding connected or not, then the gas/water supply pipes are probably plastic and therefore not providing any earth.
Contact the DNO to sort their cable

If there was an issue with the earth coming from the DNO lead sheath, what would the DNO do, convert the supply to TN-C-S or is it more complex for them than that?
 
If there was an issue with the earth coming from the DNO lead sheath, what would the DNO do, convert the supply to TN-C-S or is it more complex for them than that?
Hi Pete - if the DNO provide the means of earthing to an installation then they will maintain it if asked. But reading the thread it's not clear to me if it's genuinely DNO or some historic home brew. Anyway, DNO may choose to convert to PME and they will consult their records / inspect their local infrastructure to see its set up ready for it.
 
If there was an issue with the earth coming from the DNO lead sheath, what would the DNO do, convert the supply to TN-C-S or is it more complex for them than that?

The last TNS installation I worked on with a bad earth, I advised the client to contact WPD and have them sort it.

Their official line was "we don't support TNS anymore". The engineers went to the client site, test the earth and concluded it was garbage and advised that I move the bonding clamp up the cable (it was a normal bonding clamp on the armour/pitch outer sheath) to the lead just below the service head or fit a rod.

I have no idea of the history of the earth for the property, but as far as they were concerned, it wasn't really their problem.
 
Ideally ALL installations should have some thing like this....
View attachment 40139
....to make testing easier.

Tricky -too neat a solution .
( If some one has to un-do / leave another wire dangling/cut a wire )
"To clear a problem".
They are more inclined to feel-doing it WRONG..
( "THEY" --- Usually own a pair of spurs )
 
Last input on this thread from me

Post 19 Chris mentions bonding out of interest only.

We all read and interpret things differently. This is my interpretation.

Please agree to disagree.
Not 100% sure what you’re going on about or what it is you disagree with.
Simple question: What is the title of this thread.
More complicated question: What if anything do you understand Ze to be?
 

Reply to Rather High Ze with all the bonding in place in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
This lesser known technique can be used for RCBO protected circuits, allowing a high current test to be used. It's a good one to have in the bag...
Replies
13
Views
3K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
841
Just recently I was looking at a WPD quote for a new supply and was quite surprised to see they now quote a max Ze of 0.48 for TNCS ! [Unless it...
Replies
9
Views
4K
  • Question
I know you’ve all be waiting in suspense for the next exciting update in this story. I promise this one will be much shorter! The OH was back at...
Replies
21
Views
4K
  • Question
The DNO have been out this morning and said that the connection is PME, and both the braid and wire together are part of the system. They've...
Replies
24
Views
7K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks