Joined
Dec 24, 2016
Messages
404
Reaction score
82
Location
london
Carrying out an EICR on a property in london, the supply is a TN-S supply with an incorrect tenby earth clamped around the PILC Sub mains cable.
Long lead tested all the main bonds and i am very surprised to still get such a high reading with these parallel paths in place.
3.25ohms
With the bonding disconnected 3.25 which remains relatively the same with the bonding connected again

Would i be correct in saying the DNO will need to be notified and called out?
 
Last edited:
If there was an issue with the earth coming from the DNO lead sheath, what would the DNO do, convert the supply to TN-C-S or is it more complex for them than that?
Hi Pete - if the DNO provide the means of earthing to an installation then they will maintain it if asked. But reading the thread it's not clear to me if it's genuinely DNO or some historic home brew. Anyway, DNO may choose to convert to PME and they will consult their records / inspect their local infrastructure to see its set up ready for it.
 
If there was an issue with the earth coming from the DNO lead sheath, what would the DNO do, convert the supply to TN-C-S or is it more complex for them than that?

The last TNS installation I worked on with a bad earth, I advised the client to contact WPD and have them sort it.

Their official line was "we don't support TNS anymore". The engineers went to the client site, test the earth and concluded it was garbage and advised that I move the bonding clamp up the cable (it was a normal bonding clamp on the armour/pitch outer sheath) to the lead just below the service head or fit a rod.

I have no idea of the history of the earth for the property, but as far as they were concerned, it wasn't really their problem.
 
Ideally ALL installations should have some thing like this....
View attachment 40139
....to make testing easier.

Tricky -too neat a solution .
( If some one has to un-do / leave another wire dangling/cut a wire )
"To clear a problem".
They are more inclined to feel-doing it WRONG..
( "THEY" --- Usually own a pair of spurs )
 

Reply to Rather High Ze with all the bonding in place in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
388
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
970
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
957

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top