Good evening, it's been a while since I've posted on here but I'm looking for a little advice.

I'm doing a job this week, it's a tt supply and I'm bringing a sub main to an out building sub c/u which will supply lights sockets, and also a leg that will run to the end of the garden to a decking area where an outdoor socket will go.

I'm going to protect the sub main with a 25a rcbo, my question is will I be fine with sub c/u not containing an rcd main switch, as this will be in series I didn't want any nusance tripping.

I've done my cable calculations and volt drop ect and sized the cable at 4mm/1.5mm swa because of the long run. The ze is 50ohms
 
It's a tt earthing system, I know I don't have to make a separate tt system at the submain, just wondering is the rcbo will be enough for the circuits on the submain aswell as the submain it's self
 
It's a tt earthing system, I know I don't have to make a separate tt system at the submain, just wondering is the rcbo will be enough for the circuits on the submain aswell as the submain it's self
Add an RCD on the end of the CU covering al the circuit fed from it, or are you intending to supply a socket prior the CU ie run a cable from your house to a socket and then to the CU???, or two circuit one feeding the CU and the other feeding the deck area??
 
Unless the RCBO is single pole switched neutral or double pole then you will also trip the time delayed RCD as the neutral will remain connected in the event of a fault. You will struggle to find a SPSN RCBO or DP RCBO in single module form...only one I know of off the top of my head is SBS.
 
No there's no socket prior to the sub c/u and sorry the size of the cable is 4/2.5 lol fat fingers on a small phone, the length of the run in its entirety is 65 meters, I'm also aware the time delayed rcd tripping if not double poled, and in response, it's not, it's an old moeller board, this is why I was wondering if the rcbo at the main board will protect the sockets ect after the sub main
 
No there's no socket prior to the sub c/u and sorry the size of the cable is 4/2.5 lol fat fingers on a small phone, the length of the run in its entirety is 65 meters, I'm also aware the time delayed rcd tripping if not double poled, and in response, it's not, it's an old moeller board, this is why I was wondering if the rcbo at the main board will protect the sockets ect after the sub main
I really thought you intended to put a socket prior to the CU ap,ologies if I misunderstood, how do you intend to supply the supply to the deck area?
 
There will be further decking and a longer run, I measured the garden at 89meters but I'll be ending the run at a out door socket at 65, just future proofed it, and yes there will be a socket but not prior to the board, it will be at the end.
 

Reply to Rcbo and rcd in series in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
819
This is the point of having a trainee badge... it allows you to ask simple questions without the critism reserved for have-a-go heroes. Things...
Replies
5
Views
353

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top