S
sparkside1
Hi all
Have a problem with a Wylex 32A Type C RCBO that has tripped to a utility room and heating plant room to a west London mid terraced house.
It will not reset even with all loads removed. I tried swapping the line and neutral conductors to an adjacent same rated RCBO and the same happened. I tested the ring between L-N at the utility sockets and incoming spur to the plant room and was 0.42 ohms. I only had time for a quick look on xmas eve and will return on Monday to carry out further tests. But not having had many issues with RCBO's I need some advice on how to test these devices properly and what the possible causes could be. There is no history on this fault as the property is vacant and the problem miraculously appeared!
Cheers
Well he got 0.42 ohms from something. Could have been anything of course, no mention of whether that was a continuity reading, IR, Ze, Zs....nothing.
give the guy a bit of slack, lads. he's said it's his boss's house. boss has probably asked him to have a quick look. most likely on his way home for a freebie. he's had a quick look and is now seeking pointers. which he's had. now let him go back, find the fault and, hopefully, report back as to what it was.
Trev..tell me bud, how do you get a Zs value from a dead circuit exactly? Read my posts before commenting
The job is not a freebie the boss pays for it.
I have calibrated testers.
Telectrix..spot on for getting it
can see trev's point , though. you stated a 0.42 resistance reading, but did not explain very well. face to face, you'd have had a reply 0.42 ohms what? on a forum, it's difficult to see what you mean without a full explanation. my irish grandmother might have known, being the seventh daughter of a witch, but otherwise it's guesswork.
You know since reading that I have come to the conclusion that YOU may be (very) distantly related to Tidyboiler!!
Now THAT'S scary!!
The 0.42 ohms reading was the highest reading taken between cross connected L and N and measured at the furthest point which was a spur for a gas boiler. I dodn't get a chance to take an R1+R2 or IR test. My tester is a megger mft1720 by the way.
... and it's Christmas - the season of good will & all that so cut the poor sod some slack.
Next week, Christmas will be just a distant memory and you can rip him a new one then!! :)
Are you saying that you cross connected L&N? What were you hoping this test would tell you in relation to this fault?
Zs from a dead circuit is easy, you just use the alternative Zs testing method.
With the breaker open connect L to E at the far end of the circuit, test between the live and dead side of the breaker.
Simples!
As to how this could help you identify the fault, I am not entirely sure at the moment.
As far as your original post and the fault goes I would suggest that you did ask a bit of a daft question, you said the fault moved to with the circuit when you connected it to another RCBO so logically the fault must be on the circuit and not within the RCBO.
To properly test the RCBO you test it the same way you would a seperate RCD unit using the RCD test function of an MFT or a seperate RCD tester.
For general fault finding I would strongly recommend an analogue insulation resistance tester, it is much easier to work with a needle than a digital display. It doesn't have to be expensive or even calibrated if all you are looking for is the yes/no/maybe rather than measured values.
(And just in case anyone is wondering, yes I have been reunited with my happy pills this evening)
Sorry Parkside you are reported for abuse... if you feel others have done the same to yourself then use the report symbol at the bottom L/H of the post in question (the triangle)...
Reacting with agressive and immature language is not on regardless whether suggestive or not!... this is in the public domain and free to view by anyone on the internet, so please respect anyone may read your replies.
RCBO not restting
sparkside1,
Geordie Spark,