Im scratching my head here at this, its probably because of the time off night but i cant get my head round this at all, here in the picture is a contactor for the outside lights, now this is one of many contactors throughout the building. there is contactors at each consumer but there is 1 Photocell controlling everything,so all the contactors was linked out to bring them in at the same time. Now every circuit is on its own RCBO, you will notice that they have joined all the neutrals in a connectore block, wouldnt that affect the RCBOS? as they are all coming from different circuits??
 
Think about it, ....the neutral is common to all 3 phases, so the sensing circuit won't see any imbalance. You can have a whole 36 pole 3 phase board with all single or multi phase RCBO's protecting every circuit, ....no tripping!!!
 
No, but they're not borrowing neutrals. Just imagine in your head that all neutrals in that building are connected to one HUGE neutral bar. (even though you view it as different neutral bars in the building.) so each RCBO neutral fly lead after going through the electronics is connected to the same neutral zone regardless of different boards hence no inbalance no tripping

Sent from my GT-I9100 using Tapatalk
 

Reply to the thread, titled "Rcbo???" which is posted in Australia on Electricians Forums.

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

Daily, weekly or monthly email

Back
Top