So had to fit a new shower as old one kept tripping the rcd after few seconds assumed the shower was to fault as made a buzzing noise and tripped, on fitting the new shower it had same faukt so checked pressure of water no issue then checked wiring at box also no issue so moved onto next possibiliy of short on cable.
Yes maybe should of used multimeter and tested each one out but easier as short run in walls so run new cable exactly the same.
So decided to wire a small flex with bulb holder on that trips rcd changed the 40amp mcb to a 16 amp tried light also trips could this be a faulty rcd its rated 80amp 30ma, we also tested the the curcuit with every mcb turned off with only shower circuit on and also tripped.

Any help would be greatly appreciated as would like to think in a 6 bedroom house with each room occupied that of rcd was faulty then it would trip as currently has approx 8 circuits on and only randomly started to happen nothing new has been added.

[ElectriciansForums.net] Rcd advice needed faulty or fault
 
If the Rcd was faulty I would expect the same tripping problem for other loads that are used on circuits on the Rcd side of the board

I would expect to find a neutral-earth fault on the shower cable,but without having at least a insulation resistance tester you may be a long time finding the problem
 
You know what don't care I can't here to ask a question just because I'm not qualified doesn't make me incompetent of knowing what I'm doing working with someone who's qualified from a young age and being overseen and checked on standards of work and also working on 3 phase and also being more than competent of doing so is more than some newly qualified electricians have in experience.
As most newly qualified electricians just goto college learn sit a test and have a certificate being trained alongside a family member rewiring houses at weekends and then working doing air conditioning from the age of 14 until I was 19 and being trained to a standard by a qualified person is more than anything on a piece of paper and all on this forum are so stuck up there as**s that I'll seek advice on a different forum
 
If the Rcd was faulty I would expect the same tripping problem for other loads that are used on circuits on the Rcd side of the board

I would expect to find a neutral-earth fault on the shower cable,but without having at least a insulation resistance tester you may be a long time finding the problem
Thanks for the helpful respose I cannot see a neutral earth fault as it's literally a single cable of 6 feet brand new
 
... dads fully qualified also worked doing electrics for both single phase and 3 phase air conditioning installs he is 18th edition certified and have been trained to the qualified standard of him.
...
As he's fully qualified, what thoughts does your dad have on this situation?
 
As he's fully qualified, what thoughts does your dad have on this situation?
No longer speak to me dad had a falling out a couple of years ago after a family member had a stroke and all he wanted o know is how much money he was getting left if they passed away I've messaged a few sparkys I know but thought I would try the forum as process of elimination before messaging one as worse comes to worst they will get called out
 
It's likely that there is a N-E fault somewhere (anywhere) on the installation (not necessarily on the shower circuit) which results in a parallel path for the return current from any part of the installation. Depending on the resistance through the fault it's likely that only when heavy loads are on, such as the shower, will sufficient current divert to earth through the fault to trip an RCD.
Of course with the OP's wealth of experience and competance he will already have considered this.
 
You know what don't care I can't here to ask a question just because I'm not qualified doesn't make me incompetent of knowing what I'm doing working with someone who's qualified from a young age and being overseen and checked on standards of work and also working on 3 phase and also being more than competent of doing so is more than some newly qualified electricians have in experience.
As most newly qualified electricians just goto college learn sit a test and have a certificate being trained alongside a family member rewiring houses at weekends and then working doing air conditioning from the age of 14 until I was 19 and being trained to a standard by a qualified person is more than anything on a piece of paper and all on this forum are so stuck up there as**s that I'll seek advice on a different forum
You may know the basics of installation, be it domestic or industrial, but if you've not got basic understanding of what you're doing, its nothing but labouring.
Hands on, understanding and experience are the three basics. Lacking in any is lacking, full stop. (not an intentional reference to the lack of punctuation, by the way)
 
It's likely that there is a N-E fault somewhere (anywhere) on the installation (not necessarily on the shower circuit) which results in a parallel path for the return current from any part of the installation. Depending on the resistance through the fault it's likely that only when heavy loads are on, such as the shower, will sufficient current divert to earth through the fault to trip an RCD.
Of course with the OP's wealth of experience and competance he will already have considered this.

Yeh I understand this however with the switch disconnected and a choc block with just a flex with light fitting there should be no extra load on circuit ie should work fine on the 16amp mcb and not trip.
I would understand if the shower was on and tripped but with a light bulb on didn't as would prove that there was too much drain on circuit to trip rcd of current load was overloading circuit.

However if rcd was faulty then it would surely trip with load of house appliances and rooms etc this is reason was asking here of anything else that could be worth testing before paying for it to be investigated to be told well yeh its something we have over looked .
 
Yeh I understand this however with the switch disconnected and a choc block with just a flex with light fitting there should be no extra load on circuit ie should work fine on the 16amp mcb and not trip.
I would understand if the shower was on and tripped but with a light bulb on didn't as would prove that there was too much drain on circuit to trip rcd of current load was overloading circuit.

However if rcd was faulty then it would surely trip with load of house appliances and rooms etc this is reason was asking here of anything else that could be worth testing before paying for it to be investigated to be told well yeh its something we have over looked .
Ramp test RCD's and IR test the whole installation. It'll either be a faulty RCD or a N-E fault anywhere on the installation, assuming neutrals are correctly connected in the DB
 
. . . .
Yeh I understand this however with the switch disconnected and a choc block with just a flex with light fitting there should be no extra load on circuit ie should work fine on the 16amp mcb and not trip.
I would understand if the shower was on and tripped but with a light bulb on didn't as would prove that there was too much drain on circuit to trip rcd of current load was overloading circuit.

However if rcd was faulty then it would surely trip with load of house appliances and rooms etc this is reason was asking here of anything else that could be worth testing before paying for it to be investigated to be told well yeh its something we have over looked .
oh dear!!!
 
Been doing electrics since the age of 10 mate dads fully qualified also worked doing electrics for both single phase and 3 phase air conditioning installs he is 18th edition certified and have been trained to the qualified standard of him.
I also run all the electrics in the house when was converted in the property it located in and as you can see was fully inspected and checked by a fully qualified electrician and signed off as you can see in the picture of the fusebox I am more than capable of checking things out.
Also I have checked all earths neutrals and lives on the mcb
Please can you tell me what is in it so do I have to install earth rods.
 
Having worked with a qualified electrician for many years you will obviously be fully aware of the basic testing procedures and understand that a multimeter will often give false readings on this kind of thing.

So in light if this can you tell us the insulation resistance of this and all other circuits connected to the RCD?
 
Having worked with a qualified electrician for many years you will obviously be fully aware of the basic testing procedures and understand that a multimeter will often give false readings on this kind of thing.

So in light if this can you tell us the insulation resistance of this and all other circuits connected to the RCD?
Plus safe isolation and not reliant upon marigolds.
 
You know what don't care I can't here to ask a question just because I'm not qualified doesn't make me incompetent of knowing what I'm doing working with someone who's qualified from a young age and being overseen and checked on standards of work and also working on 3 phase and also being more than competent of doing so is more than some newly qualified electricians have in experience.
As most newly qualified electricians just goto college learn sit a test and have a certificate being trained alongside a family member rewiring houses at weekends and then working doing air conditioning from the age of 14 until I was 19 and being trained to a standard by a qualified person is more than anything on a piece of paper and all on this forum are so stuck up there as**s that I'll seek advice on a different forum
I disagree, the price of paper is very important, as is the practical training and experience
 
I disagree, the piece of paper is very important, as is the practical training and experience

Not saying the piece of paper isn't important but it wouldn't come to use as I don't wanna be a sparky and would be a waste of time and money so cannot justify costs to needing it.

As I say I got asked to do a favour to change a shower then as it wasnt that got asked if I could have a look at electrics as I have helped my friend many of times always been Checked after and signed off by professional unless it' changing sockets or lights for him.
I am currently a mechanic dealing with fault diagnosing and ecu programming so getting paper for me is not really needed
 
For the love of God it’s easy to test whether the rcd is faulty...test it with right equipment (and knowledge).

This thread smells fishy, and I don’t mean the contents of Baldrics Apple crumble.......

The idea of this post is to find out if the rcd could be the possible fault or if it could be a fault somewhere else but surely with one wire direct feed when switched off the rcd doesn't trip meaning there shouldn't be a fault on the other circuits as it' been fine for over a week.
 

Reply to Rcd advice needed faulty or fault in the UK Electrical Forum area at ElectriciansForums.net

Similar Threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
561
  • Question
Thank you for taking the time to help explain this - much appreciated
Replies
7
Views
698
In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
447
davesparks
D
  • Question
One of those backlight Chinese testers may have helped that’s if the tester didn’t catch fire or electrocute you. LED TV Backlight Tester 12W LED...
2 3
Replies
68
Views
4K
  • Question
One of the things to consider with lamp holders that have lamps missing is that there is also a neutral pin, shoving your fingers across those...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top
AdBlock Detected

We get it, advertisements are annoying!

Sure, ad-blocking software does a great job at blocking ads, but it also blocks useful features of our website. For the best site experience please disable your AdBlocker.

I've Disabled AdBlock    No Thanks