Thought I would check my DB (which has been in about 5 years) and see if calcs work out. Please advise if I have worked out correctly.
Main switch 100A this feeds
- 8 MCBs 32A x 1, 16A x 2, 20A x 1, 6A x 4
Working on 100% of highest rating circuit (32A) then 40% of remaining circuits (208A @ 40% = 83.2A) giving a total of 115.2A which is higher than main switch. Therefore my DB is out of existing regs?
- RCD 80A then covers 5 more MCBs 32A x 3, 20A x 1, 16A x 1
Thanks for your patience!
But what are the design currents of the circuits themselves.
For example, a lighting circuit, although it is on a 6A breaker, may not be drawing 6A. These are the figures you need to use for your calculation.