Back again!

Thought I would check my DB (which has been in about 5 years) and see if calcs work out. Please advise if I have worked out correctly.

Main switch 100A this feeds

  • 8 MCBs 32A x 1, 16A x 2, 20A x 1, 6A x 4

  • RCD 80A then covers 5 more MCBs 32A x 3, 20A x 1, 16A x 1
Working on 100% of highest rating circuit (32A) then 40% of remaining circuits (208A @ 40% = 83.2A) giving a total of 115.2A which is higher than main switch. Therefore my DB is out of existing regs?

Thanks for your patience!

But what are the design currents of the circuits themselves.

For example, a lighting circuit, although it is on a 6A breaker, may not be drawing 6A. These are the figures you need to use for your calculation.
 
Hi JUD,

The DB was in before I started thinking about becoming a Sparky so I guess the design currents would have been calculated using diversity guidelines, this in turn would determine which size MCB is required I guess.

I was hoping that there would be some calculation, based upon the existing MCB ratings, which could be applied to determine whether there was any remaining capacity on the main switch?

Cheers
 

Reply to RCD Calculations in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
378
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
949
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Stick the socket in a large plastic wall box with hinge and padlock. Give customer letter with key...
2
Replies
17
Views
4K
I've put a 2 way unit inside kitchen cupboards before now if we were re-using the original cooker supply but the customer wanted 2 x 16A ovens. I...
Replies
8
Views
437

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top