On a TT system the rcd must operate withing 0.2 seconds for many circuits. Why when we test rcd's does it not say 300ms for TN systems or 200 ms for TT systems?

[ElectriciansForums.net] Rcd disconnection time on TT
 
Why when we test rcd's does it not say 300ms for TN systems or 200 ms for TT systems?
Well, it does!
As you say, the trip time depends what the purpose of the RCD is.
For fault protection, see 643.7.1 which has a bit in the middle saying that chapter 41 stuff must be met.
For additional protection see 643.8
 
The TT 200ms final circuit is an odd one because that is for fault conditions. Since the Ra is chosen to keep voltage below 50V at 'In' then under typical fault conditions you will see almost 5*In through the RCD, leading to much faster disconnection.

That is why the usual "selective" RCD as an incomer is able to meet final circuit disconnection of 200ms (even though they typically measure 300-400ms at In), as well as achieving selectivity with 30mA "instant" ones used for additional protection.

I agreed the wording is pretty opaque :(
 

Reply to Rcd disconnection time on TT in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
259
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
744
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
738

Similar threads

Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
567
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
680

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top