Just installed a 5 way consumer unit in a garage/workshop. It's fed from a garage unit in the house. I've started testing and on the garage 5 way the RCD test is OK but the RCD unit in the house trips at the same time (apart from one random event). I'm not happy about this and a bit puzzled as I did something similar last week with no such issues. In fact I was worried that time as to which RCD would trip but only the one tested did ( I was impressed at how clever RCDs were). I didn't give it a second thought on this installation until I started testing! I've installed an earth rod for the garage so it's a TT system (first for me). The Ze on this surprised me - I was expecting to struggle to get a decent value yet I have a figure of 0.61 Ohms (yes I disconnected the CPC so no parallel paths etc when I tested Ze). All my test figures seem OK.
My question - How do I get the RCDs to discriminate? i.e. What have I done wrong?