Hi there all, many apologies as I'm new to testing so am still trying to get head around everything.

Testing an RCD today with all MCB's off I had some unusual readings which have confused me somewhat. The RCD was a Contactum 80A Type A. I was using a Kewtech KT64 and below are what it returned.

x 1/2 0 = >2000ms
x 1/2 180 = >2000ms
x 1 0 = >550ms
x 1 180 = >550ms
x 5 0 = 13ms
x 5 180 = 7ms

Doing a ramped test the tester returned a reading of >33mA

What would cause it not to trip on a x1 test yet it trips quick enough on a x5 test. I can appreciate I have missed something but what should I be looking for?

Many Thanks
 
Thanks for the quick reply, I thought the same thing and rang TLC (where I bought the RCD) they seemed quite sure that this was not the case. Is there any other possible reason or is that the only thing it could be?
 
yep. as above. it's tripping at > 33mA on ramp test, so it will show "out of limits" on x1. try the test button a time or 2, then retest. if still poor readings, replace it.
 
It was a brand new RCD, I switched it on and off a couple of times as well as hitting the test button a few times and this was still the reading after all that. I will be on to TLC first thing, really grateful for everyones help.
 
one other thing to try is to remove both L and N from the outgoing side and test the RCD directly. sometimes there is something on the circuit/s will give you false readings. otherwise, it's fooked.
 
one other thing to try is to remove both L and N from the outgoing side and test the RCD directly. sometimes there is something on the circuit/s will give you false readings. otherwise, it's fooked.


defo the test to do before running back to TLC. Make sure all the MCB's are off
 
Thanks for the quick reply, I thought the same thing and rang TLC (where I bought the RCD) they seemed quite sure that this was not the case. Is there any other possible reason or is that the only thing it could be?

What the hell would they know?? They are in the business of selling, not assessing. And they don't particularly like returns either!! Not when they can be avoided!! lol!!
 

Reply to RCD Fault (I'm baffled) in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
305
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
825
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
916

Similar threads

  • Question
It can also mean lasts or continues for two years.
Replies
14
Views
1K
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
687

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top