ahh yeah, you're right.. apologies, just saw TT and assumed 100...
ignore me, working nights has frazzled my brain
If you test from the RCD with both the Line & Neutral load side disconnected it has to be either a RCD fault or a tester fault if the coil is not tripping or seeing a imbalance in the flow. As you have already said that a N/E fault was reintroduced IMO the RCD'S are looking a good bet. My way of thinking is that whatever Earthing system the premises has makes no difference re the operation of the RCD the only thing I can see with a TT systems is doing a 5 X test which may fail with a high Ra over 330 ohms which would put the touch voltage over 50 volts and abort the test !
disconnect all load, switch RCD on test between L-N on load side and use the neutral on the live side of the RCD as the earth. not the TT earth. Does it trip? Do the same with load connected.
Reply to RCD Fault. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net
Exactly. I was going to ask on the earthing once he clears this boiler fault (suspect on internal component). OP mentions oil boiler but makes no...
Did a fuseboard change yesterday from an old wylex board to dual rcd on a TT system with 14ohms ZE and finished pretty late. Went back this...