B

bigbaddave

Right here goes,EICR report on a TT install, ZE 99 Oams. It global 58.6 meg. RCD test tho trip on x1 x5.ramp test no joy. Assumed faulty RCD change for new one again no trip.try a third one and no trip. Loop on the same socket 99.1 Oams. It's not faulty RCD as they work fine In another install. Anyone had the same issue
 
Hi yes tester is fine, tried on a few installs. the funny thing is that there was a N-E fault on the install when i turned up. The RCD was holding. After finding the IR fault changed the RCD assuming that this was faulty but new new one still no joy and again the next one didnt trip.. So just to try and confirm put the N-CPC fault back on and the RCD held... Well it did for hour or so.. then tripped and couldnt be reset as you would expect with a N-CPC fault. Took the N-CPC fault off and retested. RCD tested ok.. Then 20 minutes later didnt test ok.. put the N-CPC fault on and again didnt trip.. At each stage of the testing a ZS reading was taken to ensure that there a reading.

The N-cpc confirms that its not the tester and the testing the 3x RCD'S in differant installs confirms its not the RCD
 
Sounds like you may have a crossed neutral which is intermittently being switched on and off maybe?

Its not no, its a MAIN switch RCD and not a Duel board on this occasion im affraid

- - - Updated - - -

Good morning sorry if I'm sounding a bit slow, I've just woken up.
you mentioned this is a TT system! Is the RCD the main switch 100mA?

It is a TT however this one has a 30Ma as the main swicth and not a 100ma
 
Last edited by a moderator:

Reply to RCD Fault. in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
328
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
855
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
975

Similar threads

  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
733
  • Question
Im not as clever as you guys. I would be doing what somw others have said, I would be leaving certain items switched off for a period of time...
2
Replies
19
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top