Hi all,

I have just read an old periodic report that has highlighted a TT system that has an RCD main switch mounted in a non insulated enclosure (metal) as a category 2.
Does it state anywhere in the reg that the RCD should be in an insulated (plastic) enclosure. I've had a look but cant find anything.

Thanks

D
 
I would consider the origin as the outgoing terminals of the distributor’s meter or isolating switch, not always possible to have an RCD located here on the tails.
So therefore load side & connected tails of the dist meter would not be the origin, but would be classed as the customers equipment (as in not the origin) & this is where you would find the single rcd.

Your meter tails will comply if they are insulated & sheathed.....but will the enclosure they enter ?
Consider a class I enclosure & any fault between the origin & the terminals of the rcd (tails in contact with the earthed Class I enclosure), thats right due to the probable high Ze on a TT system will mean the rcd will not detect the fault & the suppliers cutout will not dissconnect the fault leaving the Class I enclosure and all earthed metalwork in the installation at..........................the supply voltage potential.

Class II enclosure or the insulated bushes that keep the tails seperated.


Hows that for you
 
Ok not clever, got it now thanks. That makes perfect sence. I just wish the regs were writen in english and not some strange language from a land far far away!!! Cheers.
 

Reply to RCD for TT system in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
159
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
526
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
474

Similar threads

  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K
  • Question
Good point, I was assuming an up-front RCD is for fault protection within DB, etc, and to cover for a failed RCBO for fault conditions, not as...
Replies
6
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top