bobbuild

hi, could anyone please advise me if:
i can take a feed from a spare mcb in fuse box to an rcd mounted next to it, or must i take the feed from meter tails?

i need to add some sockets to a kitchen and there is no rcd protection,
so i need to rcd the ring and not sure on how i can achieve this...
 
Last edited by a moderator:
yeah spot on cust not up for payment
so what is rules for using rcd, i can design and calculate circuit for cable sizes and mcb, even do all necc testing but unsure how to incorporate rcd into circuits, except from fusebox
not sure what you mean there,I think you are talking about how to fill in your eic/minor works cert? If your RCD is adjacent to board,you would not have to include the 6mm as details of a submain or ought.You would I'd imagine have to include a note that the rest of the installation does not comply with 17thedd.
 
hi, could anyone please advise me if:
i can take a feed from a spare mcb in fuse box to an rcd mounted next to it, or must i take the feed from meter tails?

i need to add some sockets to a kitchen and there is no rcd protection,
so i need to rcd the ring and not sure on how i can achieve this...

Just a quick point, can the current installation take the extra loading you are planning?

You have said that you are adding extra sockets is this an additional ring final circuit?
 
Last edited by a moderator:

Reply to rcd help in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
476
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
955
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
900

Similar threads

  • Question
Yes I touched on diverted neutrals when I went over guidance note 3 the first time but I’m doing a second round and going between all books whilst...
Replies
9
Views
607
  • Question
Yes Table 3A that was in Appendix 3 of the 17th edition of BS7671 and in BS 7671:2018 (Blue Book) up to the release of BS7671:2018 +A2:2022 (Brown...
Replies
11
Views
942

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top