B

bobbuild

hi, could anyone please advise me if:
i can take a feed from a spare mcb in fuse box to an rcd mounted next to it, or must i take the feed from meter tails?

i need to add some sockets to a kitchen and there is no rcd protection,
so i need to rcd the ring and not sure on how i can achieve this...
 
Last edited by a moderator:
yeah spot on cust not up for payment
so what is rules for using rcd, i can design and calculate circuit for cable sizes and mcb, even do all necc testing but unsure how to incorporate rcd into circuits, except from fusebox
not sure what you mean there,I think you are talking about how to fill in your eic/minor works cert? If your RCD is adjacent to board,you would not have to include the 6mm as details of a submain or ought.You would I'd imagine have to include a note that the rest of the installation does not comply with 17thedd.
 
hi, could anyone please advise me if:
i can take a feed from a spare mcb in fuse box to an rcd mounted next to it, or must i take the feed from meter tails?

i need to add some sockets to a kitchen and there is no rcd protection,
so i need to rcd the ring and not sure on how i can achieve this...

Just a quick point, can the current installation take the extra loading you are planning?

You have said that you are adding extra sockets is this an additional ring final circuit?
 
Last edited by a moderator:

Reply to rcd help in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
279
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
776
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
787

Similar threads

  • Question
ok cheers for the help lads
Replies
7
Views
703
  • Question
Indeed. Sounds as though the only extra load is a 20 and a 6 breaker… could just be a light and a socket… or could just as likely be a dozen...
Replies
8
Views
772

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top