So you are saying it would be more likely a faulty RCD rather than a Circuit fault? Disagree

I was disagreeing with the post that ruled out a faulty RCD ....

Tripping RCD's can be caused by:

1. Issue with the incoming supply
2. Faulty RCD's
3. Earth leakage from appliances
4. N-E faults on RCD circuits
5. N-E faults on non RCD and RCD circuits
6. Faulty appliances

etc etc
 
The shower is still working but doesn't get used? The Neutral and earth are still connected even if the MCB is switched off (others have mentioned this). When RCDs trip I always think water or poor insulation resistance. I'd be tempted to remove the shower neutral & earth (and tape up) in the first instance unless it can be totally isolated? This will eliminate that circuit without an unnecessary disruption to circuits that are being used.
It does seem odd to wire the RCD in with circuits either side rather than just to the right with one length of bus bar - looks like it's been an afterthought.
 

Reply to RCD in consumer unit keeps popping, replaced with new one, still same issue in the DIY Electrical Advice area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
223
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
683
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
625

Similar threads

I opened up the CU again and the round junction box above and what I found was the blue and brown wires coming in from the wall just above the 15a...
2 3
Replies
33
Views
2K
  • Question
Yep, that’s what I do. That spare RCD has always come in handy down the line.
2
Replies
24
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top