OP
Silly Sausage
Hi I have already narrowed down the fault to the ring circuit, with the ring circuit disconnected, the RCD holds in and the RCD test button works, I have tried the faulty circuit on the other RCD and the fault returns... RCD won't hold in with any sort of load on it, I have done an insulation resistance test showing <200M ohms between each, I have also done an end to end, r1 + r2 test, r1 + rn test, all good, I have been in every socket/spur and can't see any crossed wires. The test results does not show that anything is wrong. Surely if there is a trapped wire the insulation resistance test would indicate a fault or if there has been a crossed wire the my (r1 + rn) or r1 + r2 would indicate I have a problem????
What were your test results?
r1, rn & r2,
R1+R2 at every socket.
Zs at every socket.
I hope you've noted them all down?!