S

Snapester

Hi guys, been doing some work on a kitchen the CU is a Crabtree Starbreaker Board which has no RCD! As we all know installing to current regs requires the install of RCD?
The kitchen is fed via two circuits one radial and the other side on the ring final, the board cannot take RCBO's that i know and the only way i see of doing this is to install a separate enclosure housing an RCD and two MCB's covering the circuits in question.

What are you ideas or how have you guys gotten over this issue?

Thank
 
i've got a couple of starbreaker boards for spares. both have RCDs, if you can post a pic of trhe board that you have, they may be compatible.
 
[ElectriciansForums.net] RCD on existing circuits This is the board in question.
 
similar to those i got. trhe RCDs take up 2 module spaces though. would leave you short of space, unless you were to replace the main sw with RCD and have up front RCD, not the best way, but cheap. i'll dig the things out later and post a pic.
 
you would fall foul of the division of circuits to minimise inconvenience due to a fault tripping all circuits out. end of the day, it's your call as to what the customer will pay for.
 

Reply to RCD on existing circuits in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
295
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
804
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
839

Similar threads

  • Question
You'd have to be mindful of SPD conductor lengths doing it that way. I think Matt:E make a single board with Type A RCBO, openPEN detection and...
Replies
1
Views
989
Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
786

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top