RCD protection is not required, unless any of the appliances supplied are mobile and to be used outdoors.
Additional protection (excluding RCDs) will be required for the cables run through joists.
i.e. hole for the cables at a depth greater than 50mm, metal plate over any notches or holes less than 50mm, cable with an earthed metallic sheath, etc.
Additional protection (excluding RCDs) will be required for the cables run through joists.