Situation is: customer has installed a 6mm cable to his shed for a couple of sockets and a couple of lights. he has actually made a very good job of it, 6mm T/E in 20mm pvc conduit, all surface ( none buried.). now he wants me to supply accessories, MCBs etc. and connect up. as it's outside, i'm going with RCBO at the CU and just 2 MCBs in shed. the only down side i can see is that in the event of a trip, he'll have to walk the length of the garden and into the house to reset. apart from this, i prefer the RCD protection at source , rather than in the shed, thus protecting the 6mm. also i'm sure the regs. require RCD protection unless SWA or steel conduit is used. what are others' thoughts?
 
I assume that the plastic conduit installation of the sub-main is not, over any length, self supporting? If this is the case then on a grade of probabilities it is unlikely that any damage over a period of time will happen.
RCD protection at either end would suffice.
Personally I would have run the sub-main in SWA and provide RCD/RCBO protection for the final circuits close to the point of ulitization
 
I assume that the plastic conduit installation of the sub-main is not, over any length, self supporting? If this is the case then on a grade of probabilities it is unlikely that any damage over a period of time will happen.
RCD protection at either end would suffice.
Personally I would have run the sub-main in SWA and provide RCD/RCBO protection for the final circuits close to the point of ulitization[/QUOT

if i was running the cable, i would have uses SWA. been today, done most of the job. gone with RCBO at CU.
 
RCD at the mains for me, its a shed so no hardship to walk. rcd's only trip for a reason usually so for me its belt and braces if no earthed sheath like swa. also i put no trust in conduit down a garden in ten years where the saddle's have been ripped off the wall, that way you know when the cable has been damaged.
 

Reply to RCD or NOT in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
450
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K
I can imagine it just disappearing (loudly) under short circuit conditions, then the resulting blast/plasma etc. casing the busbars to flash over...
Replies
13
Views
709

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top