Situation is: customer has installed a 6mm cable to his shed for a couple of sockets and a couple of lights. he has actually made a very good job of it, 6mm T/E in 20mm pvc conduit, all surface ( none buried.). now he wants me to supply accessories, MCBs etc. and connect up. as it's outside, i'm going with RCBO at the CU and just 2 MCBs in shed. the only down side i can see is that in the event of a trip, he'll have to walk the length of the garden and into the house to reset. apart from this, i prefer the RCD protection at source , rather than in the shed, thus protecting the 6mm. also i'm sure the regs. require RCD protection unless SWA or steel conduit is used. what are others' thoughts?