Situation is: customer has installed a 6mm cable to his shed for a couple of sockets and a couple of lights. he has actually made a very good job of it, 6mm T/E in 20mm pvc conduit, all surface ( none buried.). now he wants me to supply accessories, MCBs etc. and connect up. as it's outside, i'm going with RCBO at the CU and just 2 MCBs in shed. the only down side i can see is that in the event of a trip, he'll have to walk the length of the garden and into the house to reset. apart from this, i prefer the RCD protection at source , rather than in the shed, thus protecting the 6mm. also i'm sure the regs. require RCD protection unless SWA or steel conduit is used. what are others' thoughts?
 
like you i prefer the protection at source so the walk to reset seems a small price to pay. Good idea from TC though as the cat sh*t gets everywhere....lol
 
As long as the 6mm is not buried anywhere I see no reason to put a RCD on it, just put a garage unit in the shed to cover things there. That's probably a cheaper option too
 
The Regs don't require that the cable be RCD protected, as it's not concealed in a wall.
What's the likelyhood of the cable being damaged?
 
I assume that the plastic conduit installation of the sub-main is not, over any length, self supporting? If this is the case then on a grade of probabilities it is unlikely that any damage over a period of time will happen.
RCD protection at either end would suffice.
Personally I would have run the sub-main in SWA and provide RCD/RCBO protection for the final circuits close to the point of ulitization
 
I assume that the plastic conduit installation of the sub-main is not, over any length, self supporting? If this is the case then on a grade of probabilities it is unlikely that any damage over a period of time will happen.
RCD protection at either end would suffice.
Personally I would have run the sub-main in SWA and provide RCD/RCBO protection for the final circuits close to the point of ulitization[/QUOT

if i was running the cable, i would have uses SWA. been today, done most of the job. gone with RCBO at CU.
 
RCD at the mains for me, its a shed so no hardship to walk. rcd's only trip for a reason usually so for me its belt and braces if no earthed sheath like swa. also i put no trust in conduit down a garden in ten years where the saddle's have been ripped off the wall, that way you know when the cable has been damaged.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

Daily, weekly or monthly email

Thread starter

telectrix

Mentor
Arms
-
Joined
Location
cheshire/staffordshire
If you're a qualified, trainee, or retired electrician - Which country is it that your work will be / is / was aimed at?
United Kingdom
What type of forum member are you?
Electrical Engineer (Qualified)
Business Name
Telectrix

Thread Information

Title
RCD or NOT
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
11
Unsolved
--

Advert

Thread statistics

Created
telectrix,
Last reply from
needasparks,
Replies
11
Views
1,430

Advert

Back
Top