HI guys,
Just doing a swa outbuilding supply for an Elecsa assesment
I was hoping for a 32a mcb to supply 6mm 3c to outbuilding but because of high zs will need rcbo on swa? I will then fit dp main switch at other end. Ideally wanted rcd at other end
cheers
Yes the SWA would need to be RCD protected. I did a similar thing recently and there's a thread i started on here somewhere. Basically if its not practical to go to the supply whenever you need to reset the RCD, then put a tie delayed 100ma RCD protecting the SWA, and put your 30ma RCD in the outbuilding
Time delay RCD's aren't cheap mind. Think I payed about ÂŁ70
You would not take regulation 411.5.2 into consideration then, which is why the OP was asking about lowering the Zs, if it;s not possible then yes he will need to RCD protect the circuit.
If the installation is all TT, you might want to try adding another rod to the system. Anyone bothered to check with the DNO to see if the supply has been PME'd in that area?? If it has, then a lot of problems could be solved!! ...lol!!
Reply to rcd protecting swa on tt? in the Australia area at ElectriciansForums.net
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...