HI guys,

Just doing a swa outbuilding supply for an Elecsa assesment

I was hoping for a 32a mcb to supply 6mm 3c to outbuilding but because of high zs will need rcbo on swa? I will then fit dp main switch at other end. Ideally wanted rcd at other end

cheers
 
Yes the SWA would need to be RCD protected. I did a similar thing recently and there's a thread i started on here somewhere. Basically if its not practical to go to the supply whenever you need to reset the RCD, then put a tie delayed 100ma RCD protecting the SWA, and put your 30ma RCD in the outbuilding

Time delay RCD's aren't cheap mind. Think I payed about ÂŁ70
 
Yes the SWA would need to be RCD protected. I did a similar thing recently and there's a thread i started on here somewhere. Basically if its not practical to go to the supply whenever you need to reset the RCD, then put a tie delayed 100ma RCD protecting the SWA, and put your 30ma RCD in the outbuilding

Time delay RCD's aren't cheap mind. Think I payed about ÂŁ70

You would not take regulation 411.5.2 into consideration then, which is why the OP was asking about lowering the Zs, if it;s not possible then yes he will need to RCD protect the circuit.
 
If the installation is all TT, you might want to try adding another rod to the system. Anyone bothered to check with the DNO to see if the supply has been PME'd in that area?? If it has, then a lot of problems could be solved!! ...lol!!
 

Reply to rcd protecting swa on tt? in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
393
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
977
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

  • Question
That was my saying not long ago about TNS to PME system. I would be nice you can ring up the DNO, will the systems being up graded, there is a...
Replies
9
Views
2K
  • Question
I think there is a little truth in what the guy in the video says, but he makes more out of it than he should. A N-E fault on a circuit protected...
Replies
28
Views
2K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top