RCD protection on a second distribution unit in work shed | on ElectriciansForums
Discuss RCD protection on a second distribution unit in work shed in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
R
RobMax
Planning on putting in a sub-main across garden into a workshed to accommodate socket circuit with workshed, garden lighting and pond pump. It will be protected at main c/u on an RCD would it also be necessary / advisable to have further RCD protection in the workshed?
rcd's inline can be problem with nuicene trippin, why not just come off mcb to new board in shed and protect withwith rcd there or rcbo..
what about earthing
well think they reccomend that, and depends on earthing system.
remember they like good discrimination of devices ratio of 2/1 is rule of thumb, like 40A breaker in house and 20 in shed .just example
You need protective devices/mcbs that are larger than the design currents but that will still protect the cables. ie the current carrying capacity of the cable, when all simultaneous rating factors have been applied, must be greater than the rating of the protective device (In).
If 2 ordinary RCDs are in series there is no discrimination between them.
As i=p/u said, it is best if you can arrange to have the rcd at the new submain - easier to test and reset, and also not taking out half the house's circuits if it trips :)
use swa to supply shed from a unprotected circuit at the origin and put 30 mA rcd in shed only and you dont need the rod unless there is extraneous conductive parts coming into the shed such as water /gas/ oil pipes etc
if using 3 core swa and the third as the cpc then only earth the armour of the swa at the origin
Did search as MarkieSparkie suggested (long thread) and will think again. Like brucelle suggestion. Thanks for all for comments.
Reply to RCD protection on a second distribution unit in work shed in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net
Regulations notwithstanding, the only thing in those pics that is likely to be affected by sheep is the trailing flexibles on the ground from the...