D

Dave 85

Hi guys

Just wanted to pick your brains on the following...
I've been doing some work in a Jaguar dealership and they've had a health and safety guy come around and recommend that all existing socket circuits and 3 phase car ramps should be given RCD protection. I have been asked to quote for said work.

Now we are looking at 10 3phase ramps and around 12 socket circuits fed from 4 different DB's (old brown square D ones) which are all 20 odd meters apart.

Ideally I wanted to replace at least 3 of the DB's so I could put RCBO protection on all socket circuits but I'm not sure what to do with the ramps....as far as I'm aware you cant get 3phase RCBO's??? and having an RCD main switch on each board seems like a very poor option.

One though is to replace the DB's, keep MCB's on the ramps but then install remote RCD isolators for each ramp. Obviously I'm trying to make this cost effective.

Any advice would be much appreciated.

Thanks
 
Sockets I can understand RCD’s. Surely the ramps are fixed, it just doesn’t make any sense.

Im not saying RCD's are a bad thing here. Even with the sockets, the factory workers should only be using them for tools that they have been trained to use.. Just my opinion..
 
id also put to them that all cost incurred due to nuisance tripping of RCD's will be passed to them as they are stipulating measures beyond BS7671..... if they agree to anything you put forward ask for it in writing too as an amendment to their original wishes.

That will make them think twice..
 
I wasn't having a go at you, just the whole idea of RCD everything.

Sorry Tony. I know you wasnt having a go at me.... Its just the way I word things, it always comes across as aggressive... and im a little ----- cat really...
 
Is everyone missing the obvious here, run the supply in armoured to each ramp, and to previous posters, no the ramps don't drop hen the power is disconnected there are latching mechanism in place for just that.


What about 4 post portable rigs with trailer plug supply.... this is a case where i would have the supply covered just been to a garage and the S/Y extension lead 3ph/400v (Yes i know i took them out of service immediately) went across the workshop and was both damaged and had lost its earth.... the OP hasn't expressed the set-up but in general for fixed set-ups i see no need for rcd cover also most newer ramps have selv control power and only have LV to motor which is usually mechanically protected ... Also to note here is only the supply to the ramp is covered by the BS7671 the ramp itself isn't.
 
I dont see the point to be honest.
We recently had a similar issue but we said the staff who would be working with the equipment in question would be part of the engineering dept and therefore did not need the rcd protection.

However where we have had to rcd protect the 3 phase gear for whatever reason we have brought 3 phase socket outlets with built in rcbo's.
 
I just want to be a fly on the wall and see the expression on the H&S persons face when Dave goes along with darkwoods post 15, and states that he will add the RCD's when he receives a written demand for them from H&S and "all cost incurred due to nuisance tripping of RCD's will be passed to them as they are stipulating measures beyond BS7671"
 

Reply to RCD protection on multiple 3 phase machines in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

  • Question
<= This The RCD looks at any current imbalance between the cables routed though it, if N is not used then no current so it matters not from a...
Replies
4
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
949

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top