D

Dave 85

Hi guys

Just wanted to pick your brains on the following...
I've been doing some work in a Jaguar dealership and they've had a health and safety guy come around and recommend that all existing socket circuits and 3 phase car ramps should be given RCD protection. I have been asked to quote for said work.

Now we are looking at 10 3phase ramps and around 12 socket circuits fed from 4 different DB's (old brown square D ones) which are all 20 odd meters apart.

Ideally I wanted to replace at least 3 of the DB's so I could put RCBO protection on all socket circuits but I'm not sure what to do with the ramps....as far as I'm aware you cant get 3phase RCBO's??? and having an RCD main switch on each board seems like a very poor option.

One though is to replace the DB's, keep MCB's on the ramps but then install remote RCD isolators for each ramp. Obviously I'm trying to make this cost effective.

Any advice would be much appreciated.

Thanks
 
There is another special risk involved here, there is a significant risk of the mini hitler on a power trip having to give the place a clean bill of health if he doesn't find something ridiculous to put on his report.
 

Reply to RCD protection on multiple 3 phase machines in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

  • Question
<= This The RCD looks at any current imbalance between the cables routed though it, if N is not used then no current so it matters not from a...
Replies
4
Views
1K
  • Question
much more information required. Is the supply to the first building a DNO supply or a sub main cable from another building ? if it is a sub main...
Replies
5
Views
949

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top