hi guys if a bank of 20 sockets wired in surface trunking on a radial circuit,these sockets would be used for computers gameboys and music equipment,my question is would they need to be rcd protected ? i know normally they would not,it's just that my mate said if protecting computers they should, i cannot find anything on this
 
I have just spoken to nappit who have confirmed sockets wired in surface trunking and are going to be used for computers do not have to be RCD protected, but have to be labelled, this will change come January 1st
How are you guaranteeing they will only be used for computers, you still haven't stated the need to avoid rcd protection.
 
This is a matter of being sensible and reasonable. If the total leakage is enough to cause nuisance tripping, it's possibly enough to cause injury. He's planning to be using the circuit for handheld devices etc where the user might be the only earth path, so rather than pretending the problem doesn't exist, a high-integrity earth is probably warranted. Correctly specced RCDs / RCBOs will not suffer from nuisance tripping, so don't put people deliberately at greater risk by omitting them.

The exemption is to deal with specific situations where the socket is only ever going to be used for a specified piece of equipment, that might need to be taken down for service or fitted after wiring is completed etc. so needs a plug, as per the roller shutter mentioned. Permanently installed networking hardware is another, where a socket is needed because the power supply is a plug-in wall-wart type, but the equipment is permanent. No-one is going to plug a vacuum cleaner with a gashed flex or damaged Game Boy power adaptor into the dedicated socket above the office ceiling in place of the network switch. A socket on the wall in a house is different - there is no valid reason for exemption.
 
I think you are treading dangerously omitting additional rcd protection on the grounds you will label them computer use on the say so of your mate. Labelling of sockets for specific use often renders them as such due to their location eg. behind a fridge. The sockets you intend to install could be used for any purpose and if the worse came to the worst neither NAPIT or your mate will be holding your hand in a court of law.
 
Thanks for your replies I'll use a rcbo
If you are worried about nuisance tripping, if practically possible, why not split the radial into 2 or 3 circuits rather than one? As Lucien mentioned, if the accumulative earth leakage is sufficient to trip the rcd then it could be dangerously high anyhow, potentially making the circuit unsafe to use. Omitting the rcd rather than re-designing the install is not the answer. It is your duty as an electrician to design any install to a safe standard for all possible scenarios.

You cannot rely on a person's "word" that nothing else will ever be plugged in. You know as well as I do that this just doesn't happen in real life.

I think you are doing the right thing by installing a rcbo
 
If you are worried about nuisance tripping, if practically possible, why not split the radial into 2 or 3 circuits rather than one? As Lucien mentioned, if the accumulative earth leakage is sufficient to trip the rcd then it could be dangerously high anyhow, potentially making the circuit unsafe to use. Omitting the rcd rather than re-designing the install is not the answer. It is your duty as an electrician to design any install to a safe standard for all possible scenarios.

You cannot rely on a person's "word" that nothing else will ever be plugged in. You know as well as I do that this just doesn't happen in real life.

I think you are doing the right thing by installing a rcbo
i did consider extra circuits but not enough room in board
 
Lack of space in the CU isn't an excuse. The circuit can be surface wired from a non RCD protected spare way in the CU to more than one RCD FCUs close to the sockets, with each RCD feeding a group of sockets.
 

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Green 2 Go Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses Heating 2 Go Electrician Workwear Supplier
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

Advert

YOUR Unread Posts

Daily, weekly or monthly email

Thread starter

Joined
Location
birmingham
What type of forum member are you?
Practising Electrician (Qualified - Domestic or Commercial etc)

Thread Information

Title
rcd protection on sockets
Prefix
N/A
Forum
UK Electrical Forum
Start date
Last reply date
Replies
68
Unsolved
--

Advert

Thread statistics

Created
deanmac,
Last reply from
brianmoooore,
Replies
68
Views
7,413

Advert

Back
Top