Hello. I'm afraid I've got a bit of a hole in my knowledge about RCD's so if anyone could reassure me/tell me I'm completely wrong about this I'd appreciate it.

Was called to a customer today to put an extra socket in his garage and found that it's fed by twin 1.5mm with no cpc, buried in conduit, from a 15A breaker on the house's RCD-protected DB. The garage is about 25m away so I think he just about gets away with the 1.5mm volt-drop wise, but obviously I need to sort out the lack of any earth in the garage.

I'm planning on just putting in an earth spike and an RCD garage unit in place of the two MCB's he has in the garage at the minute. My (possibly stupid) question is, would having a separate earthing arrangement at the garage when it's fed from an RCD-protected breaker in the house cause nuisance trips or anything in the house? There are no free non-RCD spaces in the house DB, though I suppose I could Henley block the supply if I had to.

Any other glaring holes in my plan would be gratefully received.

Thanks.
 
1. Need to get some sort of earth into the garage - absolutely nothing there now and thought TT would be easier than running another cable from the house.
2. Yes, I suppose I am, and yes, the house is 30ma.

Thanks.
 
Needs to TT the garage because there is no earth there at all, apparently.
Twin with no earth hasn't been used for many many years so I doubt the conduit will be in good enough condition to act as a cpc.

Personally I would be advising them to have a new submain run to the garage.
 
Sorry, I missed that, I see you said there is no CPC from house. Regarding RCD, you could just put Main Switch DB (Non RCD) in garage as the sub is protected. Would normally be better with RCD at Garage but probably better having that sub on RCD in this case as has no cpc.
 
Thanks both. And I think that's where I didn't understand how RCD's work. I thought that, as they measure leakage to earth, they'd need some sort of cpc in the circuit to work. I can see now that obviously that leak to earth can go through a washing machine or a dog or a person and doesn't have to be a wire. Presumably that means the proposed earth rod in the garage won't cause any problems as it just provides another potential way for a fault to leak.
 
Forget the earth rod for a minute.

Is the submain and it's conduit in good condition and safe for continued use?
If the conduit is in good condition then use it as the CPC.
If the submain and conduit are not in good condition then you need to look at the options to replace it.

Based on experience of similar installations Ive developed a picture in my mind which is not very pretty.
 
Thanks both. And I think that's where I didn't understand how RCD's work. I thought that, as they measure leakage to earth, they'd need some sort of cpc in the circuit to work. I can see now that obviously that leak to earth can go through a washing machine or a dog or a person and doesn't have to be a wire. Presumably that means the proposed earth rod in the garage won't cause any problems as it just provides another potential way for a fault to leak.
what you have to remember here ...is that if you have 2 30mA RCDs in series...the one likely to let go under fault conditions first (assuming the fault occurs on one of the garage finals)..will be the RCD thats already being subjected to a certain amount of leakage....this is likely to be the RCD top end...
 

Reply to RCD protection to garage. in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
748
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K
  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
975

Similar threads

Regarding the EV, it’s an Ohme charger which I believe has a type A RCD built in, setup would be: 50A RCBO to feed garage db Garage db has no...
2
Replies
17
Views
967
It's not the same scenario, though. Tails more than 3mtrs can be overcome by using a fused switch and rcd board, whether the earthing system is...
2
Replies
18
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top