Interested in fellow sparks opinions on this.
Client of a 15-20year old commercial/Industrial premises wants an additional 13a socket outlet installed for a specific piece of equipment, the additional wiring for this will be off a current non-rcd ring (with satisfactory Zs value) and installed not buried less than 50mm in walls.
The ring main currently supplies about 15 socket outlets for general purpose and electronic equipment. The earth leakage on the circuit is likely too high for an rcbo to be installed at db without nuisance tripping. The db has no spare ways to split the circuit into smaller radials or with a bit of rewiring smaller rings.
Bearing in mind there is no rcd protection for the entire circuit, will labelling of the additional socket outlet for a specific item of equipment suffice?
I've usually always found a way to improve the whole circuit and install rcbo at source for minor works however I don't think its reasonable in this situation.
Client of a 15-20year old commercial/Industrial premises wants an additional 13a socket outlet installed for a specific piece of equipment, the additional wiring for this will be off a current non-rcd ring (with satisfactory Zs value) and installed not buried less than 50mm in walls.
The ring main currently supplies about 15 socket outlets for general purpose and electronic equipment. The earth leakage on the circuit is likely too high for an rcbo to be installed at db without nuisance tripping. The db has no spare ways to split the circuit into smaller radials or with a bit of rewiring smaller rings.
Bearing in mind there is no rcd protection for the entire circuit, will labelling of the additional socket outlet for a specific item of equipment suffice?
I've usually always found a way to improve the whole circuit and install rcbo at source for minor works however I don't think its reasonable in this situation.