Bizarrely, BS7671 seems to be telling us to do exactly this:So when a product is faulty we alter the test parameters to ensure it passes?
not sure on the legalities of this.
the excuse is manufacturers instructions say to do this.
what takes priority b.s.7671 or manufacturers instructions?
if the manufacturers instructions are requiring a greater degree of protection or better disconnection time this is fine, but in this case it is not.
very naughty!
643.8
NOTE: Effectiveness is deemed to have been verified where an RCD meeting the requirements of Regulation 415.1.1 disconnects within 40 ms when tested at a current equal to or higher than five times its rated residual operating current.
That's 'or', not 'and'. Poorly written reg, or deliberate?