RCD test failing on a single outdoor double socket radial circuit (55.8ms on X5). All other tests ok (IR, R1+R2, ZS). Functional test of RCBO ok. Tried circuit on another RCBO and test still fails so not the RCBO.

Am I missing something obvious? Thanks
 
Is there something in the installation that may be injecting dc into the supply?
 
RCD test failing on a single outdoor double socket radial circuit (55.8ms on X5). All other tests ok (IR, R1+R2, ZS). Functional test of RCBO ok. Tried circuit on another RCBO and test still fails so not the RCBO.

Am I missing something obvious? Thanks
Have you tried testing with the circuit conductors disconnected from the RCBO?
 
What make and type of RCBO? A/AC/B???
 
Replaced the RCBOs with new ones and still having the same problem. Tried it at the socket (outdoor), and at the DB with the conductors disconnected. RCBO still failing for additional protection at 5X In (56ms).

Any ideas what could be causing this? Cheers
 
This seems to explain the problem fairly well:

Are you already using 5 x 50ma ?
 
So when a product is faulty we alter the test parameters to ensure it passes?

not sure on the legalities of this.

the excuse is manufacturers instructions say to do this.

what takes priority b.s.7671 or manufacturers instructions?

if the manufacturers instructions are requiring a greater degree of protection or better disconnection time this is fine, but in this case it is not.

very naughty!
 

Reply to RCD Test Failing in the Electrical Testing & PAT Testing Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
299
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
807
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
850

Similar threads

Duh!!! Just re-read Op's original post, it was converted to a RFC!
Replies
12
Views
685
Continuity of the suspect cable appears fine all cores, from this I could work out the length of it and it really doesn’t appear looking at the...
Replies
2
Views
332

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top