RCD test without RCD | on ElectriciansForums
Discuss RCD test without RCD in the UK Electrical Forum area at ElectriciansForums.net
J
jonesyc894
Is there anyway I can test an installation without an RCD so I can be sure when I changethe board the RCD will trip in time? Or calculation, such as V/R eg 230/Zs.????
^^what he said, about what they said ^^
wonder if the OP will return...
About as much chance as Gary Glitter making one to the charts
Since the maximum Zs required for a 30mA RCD to trip is 1667Ω as this meets the RA x Idn <= 50 V, you can ensure that the disconnection times will be met before installing an RCD.
Being able to test the RCD to ensure correct operation by disconnection within 40ms at 5 x Idn is not possible without the RCD.
Normally the questions around RCD's are
If I change the fuseboard how can I be sure the RCD will hold etc etc so this is a new one!
Looking at the ops previous posts he is working as a electrician so I hope this is just a blonde momment question!
Reply to RCD test without RCD in the UK Electrical Forum area at ElectriciansForums.net
It can also mean lasts or continues for two years.
Ok I’ll try this when I’m down