Hi

Ive got a question regarding RCD tests.

If a DB had 7-8 ccts on MCBs all covered by a Main RCD, should we do only one cover-all test on the main RCD, or record an individual RCD test for each circuit?

Other sparkys on my firm have been doing an RCD test for each circuit, effectively testing the same RCD 8 times.

What is the correct procedure?

Thanks
 
you test the RCD the specified 6 tests
x 1/2
x1 @0deg.
x1 @ 180
x5@0
x5@180
test button
preferably with all loads disconnected and test @ the RCD outgoing terminals, and only once.

your mates are either confused or dragging the job out.
 
Pretty much looks that way. Glad I questioned it because no one else at my firm seems to have picked up on it and I know for a fact the boards they are testing arent laden with RCBO's
 
A Rcd has operating characteristics that will apply to all the circuits,if its tested at source,the readings apply to all those circuits off that Rcd

Testing separately and externally for each circuit and including those circuit properties may show incorrect operating values
 
you test the RCD the specified 6 tests
x 1/2
x1 @0deg.
x1 @ 180
x5@0
x5@180
test button
preferably with all loads disconnected and test @ the RCD outgoing terminals, and only once.

your mates are either confused or dragging the job out.

Except, for instance, MEM RCBO's which don't like being tested at the terminals .....
 
it is easier to use a socket, and complies with the "no live working" wimp brigade.
 

Reply to RCD Testing Confusion - Help! in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
771

Similar threads

Also use a tails gland and clamp if available and make sure tails are secured to a wall. The danger here is a live to earth fault in the Consumer Unit
Replies
7
Views
568
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
724

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top