H
hawk666
hi guys , all i want to know really is why we test at 0 degrees and 180 degress of the sine wave when testing the rcd , cheers guys
Isn't resistance measured in ohms? Or have I missed an update somewhere?Just remember that RCDs are fault protection
It protects 2 situations:
Human coming into contact
Fault between Line/neutral and Earth
With the human contact - the resistance of the body is over 150mA (with the average human) therefore tripping in 40ms
With a fault between L/N and Earth there could be a very high resistance of 30mA (e.g. insulation of cables) but not high enough to maintain a high enough resistance to prevent any short between L/N and Earth.
These will trip 300ms (or 200ms).
Yes for direct shorts it will trip in 40ms
an RCD must be tested at 0 and 180 to ensure
1. correct operation on both halves of the AC cycle
2. correct operation when used on DC supplies
3. the integral test button operates the RCD smoothly
4. correct polarity of the supply