Hi All,

Getting a bit confused here, do you record the 5*I or I disconnection time on the EIC cert?

Cheers
 
Sorry should have made that clear, using the basic IEE certs that you can print off from a PDF. It only has one box to record and says refer to note 13 but it doesn't clarify any further. Thanks in advance
 
Note 13 says' The operation of RCDs shall be tested by simulating a fault current , independent of any test facility in the device. Record operating time in column 13. Effectiveness of the test button must be confirmed'

What do you think?
 
I would suggest that 1xI is the result that should be recorded as this is the fault current that will cause the RCD to operate.
 
record the 1x1 which should be the highest trip time obviously if you have a trip time over 40ms on either 1x1 5x1 you would have to check your rcd or meter
 
page 82 16th edition on site guide 11.5 wher an rcd or rcbo with a rated residual operating current of 30ma is used to provide supplementary protection against direct contact with a test current of51 n the device should open in less than 40ms, unless the the protective conductor potential rises by less than 50v
regards
 
yeah, got that. 40msec at x5. but what about x1? i was always under the impression that the max. trip time at x1 was 200msec.
 

Reply to RCD Times on EIC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
792
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
818

Similar threads

Thanks for the advice, I actually had no idea about the HMO licensing rules so have learnt a lot. Just did a search, its not licensed as an HMO...
Replies
5
Views
393
So, I’m more aiming for the domestic setting myself and I don’t plan on EICR straight away. I am almost certainly not aiming for the industrial...
Replies
3
Views
364

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top