You should also be aware, if you don't already know, that the RCD must be tested x 1/2 rated trip current, x1, and x5, at 0 degrees and 180 degrees, then mechanical test button, so 7 tests in all. I am refering to the 30ma ones used in domestic, there are other RCD's available.