You should also be aware, if you don't already know, that the RCD must be tested x 1/2 rated trip current, x1, and x5, at 0 degrees and 180 degrees, then mechanical test button, so 7 tests in all. I am refering to the 30ma ones used in domestic, there are other RCD's available.
 
page 82 16th edition on site guide 11.5 wher an rcd or rcbo with a rated residual operating current of 30ma is used to provide supplementary protection against direct contact with a test current of51 n the device should open in less than 40ms, unless the the protective conductor potential rises by less than 50v
regards


We are on the 17th now
 
yeah, got that. i have always gone with 200msec as a guideline until a friendly factory electrician copied the brb for me.he was writing for hours. lol
 
I think there should be another columb x1 x5 and Ramp , be so usefull when an inspections do a few years after to see if the RCD ramp test is still tripping as recorded
 
good point nick. seems very few of us bother with ramp test except when there is a problem e.g.nuisance tripping. be good to see box on a cert. for ramp test.
 
yeah, got that. i have always gone with 200msec as a guideline until a friendly factory electrician copied the brb for me.he was writing for hours. lol
sorry lads i was miles away
300ms max @x1 40ms@x5
hope your factory electricians really freindly he may have to copy from the bgb if the new regs comes out.
how many of you want to sit that again after having just sat the last edition within the last 2years
 
I wouldn't worry Mad Frankie, it's only an amendment coming out next year so there will be no exam.
The 16th edition had several amendments during its 17 year history.
 
I wouldn't worry Mad Frankie, it's only an amendment coming out next year so there will be no exam.
The 16th edition had several amendments during its 17 year history.
we will still have to purchase a new book
your mate better ask santa for some pencils.
 

Reply to RCD Times on EIC in the Periodic Inspection Reporting & Certification area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
791
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
817

Similar threads

Thanks for the advice, I actually had no idea about the HMO licensing rules so have learnt a lot. Just did a search, its not licensed as an HMO...
Replies
5
Views
393
So, I’m more aiming for the domestic setting myself and I don’t plan on EICR straight away. I am almost certainly not aiming for the industrial...
Replies
3
Views
364

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top