RCD to outbuilding | Page 2 | on ElectriciansForums

Discuss RCD to outbuilding in the UK Electrical Forum area at ElectriciansForums.net

Joined
Jan 12, 2012
Messages
5,246
Reaction score
2,743
Location
Norfolk
Just after some opinions on this scenario...
Existing 6mm T&E leaving an existing CU (with an RCD protecting all circuits) in conduit, through a loft and out across a 3ft gap into a garage. Garage has a 30mA RCD board itself so at the moment no discrimination.
Now fitting a high integrity board so was planning to take the supply off a non-RCD protected MCB, surface mount the cable in mini-trunking (as it would be less than 50mm deep otherwise) and leave garage as-is.
I'd be interested in peoples opinion of "non-RCD protected cable for discrimination purposes" versus "All cables RCD-protected but no discrimination for garage", in other words added safety versus inconvenience if earth fault occurs.
Really due to the fact that it's T&E rather than swa.
 
The only thing i would add is that i would not want anything being plugged in from the garage and the external bit of cable on an RCD that could knock off the whole house. So i would go for no RCD MCB to avoid any nuisance tripping of the house. What gets plugged into garage sockets, like garden stuff, welding set, should not be affecting the house RCD wise. From my experience of meeting RCDs in series both at 30mA it nearly always appears to trip the house first. Law of the sod maybe or some science i dont know
its all about accumilated earth leakage when you have 2 30mA RCDs in series mate......the RCD at the house (supply) end will be subjected to accumilated earth leakage on ALL final circuits on that side of the C/U in the house......and so it will let go before the garage RCD...which isn`t being subjected to the same value of accumilated earth leakage......
 
its all about accumilated earth leakage when you have 2 30mA RCDs in series mate......the RCD at the house (supply) end will be subjected to accumilated earth leakage on ALL final circuits on that side of the C/U in the house......and so it will let go before the garage RCD...which isn`t being subjected to the same value of accumilated earth leakage......
Makes sense - so basically a waste of time fitting one in the garage
 
Makes sense - so basically a waste of time fitting one in the garage
no..no and no again.....as a garage socket may be used for outdoor equipment....several ways to deal with RCDs in series....depending on the earthing arrangements
If a TN system then no upfront RCD would be required if you use an armoured cable....you would however use an RCD downstream..(garage)...

If a TT system then a high integrity C/U can be used with a 100mA s type RCD on its own.Then use a 30mA RCD at the garage end....this will give you the discrimination you need.....
 
no..no and no again.....as a garage socket may be used for outdoor equipment....several ways to deal with RCDs in series....depending on the earthing arrangements
If a TN system then no upfront RCD would be required if you use an armoured cable....you would however use an RCD downstream..(garage)...


If a TT system then a high integrity C/U can be used with a 100mA s type RCD on its own.Then use a 30mA RCD at the garage end....this will give you the discrimination you need.....


Dont panic, was referring to the situation where the house is already covered by an RCD at 30mA, unless the garage cct comes away from rcd protection whats the point if the house always trips first because of other house leakage reducing the threshold of the house RCD.
 
It will not always be the house first, the balance of probability is the RCD with the most circuits on it but the variability in the operating characteristically could invalidate this.
If a garage RCD trips at 18mA and the house at 26mA then the garage could go first. Then you have the response time if the house one trips in 100ms and the garage in 12ms the garage one could still go first.

And obviously vice versa, could be always the house.

There is no discrimination, similarly if you have a normal 100mA at the house and 30mA at the garage and the garage one trips slowly the 100mA could go first.
 

Reply to RCD to outbuilding in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
257
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
739
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
721

Similar threads

He said something about a fused something as the lights hardly take anything .. I told him was mostly cordless tools so just chargers ..told him...
Replies
11
Views
604
  • Question
This charger doesn't support rear entry from the looks, only bottom entry, hence that. Unless they make a white sheathed SWA, I would still need...
Replies
8
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top