Just been called out investigate RCD tripping on downstairs ring at my parents it just went in the early hours with no history. Have unplugged all appliances from the 10 sockets on this ring and switched all sockets off. There are no other appliances fed from this ring other than those plugged in via sockets. There are 3 other circuits protected by the same RCD in the CU ie Shower, Cooker and upstairs ring, these are all functioning normally and don't trip the RCD. I have substituted the downstairs ring MCB but the circuit still trips the RCD immediately when the MCB is switched on with nothing plugged into the sockets. My next step is to disconnect the ring, split the dead ring at the midpoint and test each half, but before doing this I removed the 2 CPCs for the ring at the CU from the earth bar and the circuit now stays on and doesn't trip. Before I plough on , disconnect the phase and neutrals and do dead circuit testing is there anyway that I can identify why the disconnection of the CPCs allows the ring to operate? Graham
 
Looks like an all insulated ring with no parallel paths and earth from the cpcs only.
Then leakage through maybe dampness. Underfloor joint box, painters been using a steam stripper and water running into the sockets, dampness by other route to sockets on external wall etc etc.
As already stated, IR wins.

Boydy
 
Just been called out investigate RCD tripping on downstairs ring at my parents it just went in the early hours with no history. Have unplugged all appliances from the 10 sockets on this ring and switched all sockets off. There are no other appliances fed from this ring other than those plugged in via sockets. There are 3 other circuits protected by the same RCD in the CU ie Shower, Cooker and upstairs ring, these are all functioning normally and don't trip the RCD. I have substituted the downstairs ring MCB but the circuit still trips the RCD immediately when the MCB is switched on with nothing plugged into the sockets. My next step is to disconnect the ring, split the dead ring at the midpoint and test each half, but before doing this I removed the 2 CPCs for the ring at the CU from the earth bar and the circuit now stays on and doesn't trip. Before I plough on , disconnect the phase and neutrals and do dead circuit testing is there anyway that I can identify why the disconnection of the CPCs allows the ring to operate? Graham
so Graham....after removing the 2 CPCs then energising the circuit (a no no for a start)...did you expect the device to still let go?
 
This could be something as small a hole in a conductor sheath, with the bare wire touching a metallic backbox. Ive had this happen before. Check for recently hung pictures and nails which may have been inserted, into a wall perhaps, somewhere on the cable run.

If you have an RCD activating and there is no load, there has to be an earth fault in a place where you would least expect to find it...

And like GLENNSPARK says. If you disconnect the CPCs on the ring. The RCD that protects it, will not operate as it wont detect the earth fault...
 
The RCD is protecting the other three circuits and is operating under load. I was trying to understand why Babylons Burning suggests that it points to EL fault rather than say EN fault. At 8am tomorrow I will be back on the case with my trusty Fluke, split the ring and crack on. I have a feeling it will turn out to be in the kitchen, where steam abounds! There is also some evidence of mice in the kitchen and I wonder if they have been chewing on a wire. As always any other helpful suggestions welcome.
 
It could be either a LE fault or NE fault. I would definitely do an IR test and then identify which cable is giving you the problem. If it is a cable and difficult to replace, i would split the ring and have two radials if you have the room in the CU.
 
It could be either a LE fault or NE fault. I would definitely do an IR test and then identify which cable is giving you the problem. If it is a cable and difficult to replace, i would split the ring and have two radials if you have the room in the CU.

It will be a L-E fault, as the RCD trips only when the MCB (single pole) is on.

Glenn is correct, the CPC's should never be removed to fault find live, as this is a hazard.
 

Reply to RCD trip help in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
330
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
856
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
980

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
Ok I’ll try this when I’m down
Replies
4
Views
390

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top