I'm new on this site and have joined for some info on a problem which is driving me mad...
I have installed a 8.5kw shower, run a 11m 10mm t+e from the 40a MCB to a 45a on/off switch and then to the shower..but when i turn the shower on it trips the RCD on the splilt load CU and the MCB stays on..so i power it back on..removed the shower, checked the voltage and have 240Vac..but as soon as i turn the shower on again it trips..any ideas pls????
 
Its the second shower as this was happening with the new one i put in last time, so i thought it was maybe the shower?? Bought a new one and the same thing happening to this one...can i use a 40a mcb and a 45a on/off switch or do they have to be the same??

Sky diving sounds good to me lol:d
 
Will double check it later when i get in from work..if it is on the correct n bar...any ideas what else it could be? Was thinking if its the rcd that trips then its gettin an earth fault from somewhere...could be the 10mm cable as i have fitted it under floorboards and wonder if i may have caught it with a nail or something else?? But if i had then i wouldnt get voltage would i? Im convinced its a problem in the cu
 
Safely isolate the shower...Electrically disconnect shower at shower end...Get suitable terminal block, and safely terminate into terminal block...Re-energise shower circuit...If it still trips, then it is a wiring/earth fault...start at CCU to see if N on correct neutral bar...work your way through the circuit, checking each connection at all points...

If the circuit energises ok when shower is disconnected, then fault will be at the shower unit, either incorrectly connected, damaged conductor insulation touching eathed point, or faulty internals in shower.

Yooj
 
Will double check it later when i get in from work..if it is on the correct n bar...any ideas what else it could be? Was thinking if its the rcd that trips then its gettin an earth fault from somewhere...could be the 10mm cable as i have fitted it under floorboards and wonder if i may have caught it with a nail or something else?? But if i had then i wouldnt get voltage would i? Im convinced its a problem in the cu

Sounds to me like you need to do full test sequence on this circuit?

If you dont have access to test equipment then you can do as YOOJ has said but it is preferred to consult a proffessional electrician.
 

Reply to rcd trip on my shower in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
106
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
905
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

  • Question
There are two reasons for a fuse/mcb they are: 1) fault conditions - which must exist always, and be capable of operating for all points on the...
Replies
4
Views
1K
As the cable itself has had the cpc cut off at both ends I would enter a C3 as it doesn't offer any protection within the cable if accidentally...
Replies
3
Views
547

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top