Hi

I have an issue with random RCD tripping. It happens at different times of the day and no obvious cause (ie particular piece of equipment).

All connected equipment has passed recent PAT test and IR on circuit looks ok (>600M PE).

A lot of the connected equipment has thermostat controlled heating elements - wax melting machines etc (it’s a beauty salon).

Had a thought that if a couple of RCD protected socket adapaters were put on the sockets and checked whenever it tripped, Does this sound like a reasonable albeit long winded way of narrowing down the fault??

Any other suggestions??
 
if you are thinking of the plug in type, you could get some 10mA ones. if it's appliance problem that would sort it. as long as you can rely on hair-brained beauticians to plug them in.
 
I would ask the customer to keep a log of when the tripping occurs.

What's the background leakage on the circuits protected by the RCD ?

You could have high leakage and anything could tip it over ....

What are the RCD test results?
 
For us to be informed on the installation could you also tell us:

1. the type of earthing system.
2. presence and state of EP bonding.
3. computer equipment?
4. any water leaks recently?
5. what kind of lighting?
6. how for example the wax baths are supplied.
 
if you are thinking of the plug in type, you could get some 10mA ones. if it's appliance problem that would sort it. as long as you can rely on hair-brained beauticians to plug them in.

I'm not sure you could guarantee discrimination using that method.

Just out of interest,has anyone else tested any of these plug-in RCD adapters? I did,on one me dad had purchased from B&Q and the best description i could give it,would be "random" :)
 

Reply to RCD tripping a mystery in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
265
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
756
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
743

Similar threads

I e got a guy coming out tomorrow to do some proper testing, it's just driving me insane 🤣 At the moment it's probably got no more than 2kw...
Replies
7
Views
802
  • Question
Yea all out circuits were disconnected & Rcd ramped tested Think this will be the right way forward,with EL clamp meter Cheers have a nice Christmas 😎
Replies
2
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top