This thread is a week or so old, all this ground has been covered and the OP has been made fully aware of design leakage by lighting computers etc, the limitations of removing the RCD from circuits and what needs doing if it is done for fault finding purposes, also he has been made aware of the testing sequences and the quickest way to identify problem. As recently mentioned its just going around in circles.

note what hasn't been mentioned here is if the leakage is designed high earth then the RCD could be changed to a Main switch and a SI unit 30mA put up front of board, this recognises and ignore certain design frequencies and allows for a greater no' of computers etc.

In reply to Tonk a design allowance of 3mA per work point is advisable thus making a circuit only six workstations at max, 10 workstations leaves you open to the occasional nuisance tripping.
 
With regards to my SI-RCD unit suggestion, its may be a quick fix but only if it is high earth design currents, but the installations is poor by design and its this that should be addressed, with all the hours spent searching the fault, a few hundred quid to fit rcbo's and front end with main switch would be cost effective and also will identify the problem circuit if genuine fault leak exists.
 
Seems to be an IT high earth leakage thread!
I've I&Ted loads of Banks and virtually all of them had RCD sockets on standard ccts.
Made sense to me.
 

Reply to RCD tripping dilemma in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
185
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
897
davesparks
D
As someone who is in the process of registering with napit for the first time reading their response they sent to OP by email about the “eicr”...
Replies
61
Views
3K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top