Had quite a few problems lately with rcd's on dual boards tripping and on 2 occasions I haven't been able to find the problem (trips once every couple of days) . I have meggered circuits, ramp tested rcd, used megger mA meter for earth leakage etc. On both occasions there was an earth leakage of 10mA for entire board so shouldn't trip rcd. However I changed rcd to rcbo's and haven't had a call back since.
I have heard in the past people saying about external influences causing rcd's to trip. However I don't understand how this works. Can somebody explain in simple thick electricians terms how this can happen. The funny thing is with the last rcd the owner said it only started tripping since eon replaced an 11KV overhead cable.(Last one was taken down live by tatters). Thanks to anyone who has patience to explain....
 
I had a new 100mA S type on a distribution circuit that would trip before a 30mA on the final circuits when a HF fluorescent was turned on. Turned out to be a faulty 100mA RCD which was tripped by interference, a replacement from the same manufacturer had no problem.
 
It was explained in the link i give you .... if you find it hard to grasp dont worry learn to walk before you run..... the imbalance isn't a measured one you have on the load side ... its like a biased created normally on the L - E from effects like capacitance due to the PD been 230v where the same capacitance is present on the N side with little or no PD to earth the effect is small so you get a generated imbalance that the RCD core see's before you even consider your own leakage of your loads.... and i dont think you can measure it either it can be created by heavy loads switching in adjacent properties etc ....not easy to understand but as i said dont worry i doubt you'll ever see this issue due to these causes again.
 

Reply to RCD Tripping.....External influences... in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
717
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
1K
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
3K

Similar threads

In my opinion replacing the consumer unit and waiting to see which RCBO trips is not a good fault finding technique. If the lighting circuit...
Replies
8
Views
809
davesparks
D
  • Question
Assumption is the mother of all major foul-ups! Start with the basics, like IR testing, RCD testing on its own, and checking the leakage as...
Replies
7
Views
782

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top