Because you have had electricians working there at least one of them should have tested the RCD to see if it functions properly, even though they may not have done a ramp test as it is not required, this testing should have eliminated the RCD failing as a problem.
Because you have had the 24 hour supply RCD trip when the off peak heating on the off peak supply has come on this means that the fault is reduced to a supply issue or a neutral earth fault because the off peak heating should normally be unable to cause the main board RCD to trip.
If the supply does have a loose connection providing an irregular and highly variable waveform to the main board it is possible but not common for the RCD to be affected by the intermittent effect and trip, this could be initially checked, not by touch!, by observation of the supply tails at the meter and any joints before the meter. If there is a bad loose connection the tails would be getting hot and look darker than normal, possibly signs of flashes if it is dark and a high load is taken. If this is the case then it would need a rapid response to resolve the issue.
If it is a neutral earth fault of high resistance then individual Insulation Resistance
testing of the circuits on the main board should highlight the potential problem, though it would also be critical that the earth was still connected to the earthing system to check for faults to an unexpected earthed part.
The rest of the advice already given above stands.
I would be heading for the NE fault area as a cause based on what you have described.
However only personal inspection and testing would be able to identify it accurately and it may well take a long time. An electrician could also possibly suggest some narrowing down methods if the fault is not clear cut.
Because you have had the 24 hour supply RCD trip when the off peak heating on the off peak supply has come on this means that the fault is reduced to a supply issue or a neutral earth fault because the off peak heating should normally be unable to cause the main board RCD to trip.
If the supply does have a loose connection providing an irregular and highly variable waveform to the main board it is possible but not common for the RCD to be affected by the intermittent effect and trip, this could be initially checked, not by touch!, by observation of the supply tails at the meter and any joints before the meter. If there is a bad loose connection the tails would be getting hot and look darker than normal, possibly signs of flashes if it is dark and a high load is taken. If this is the case then it would need a rapid response to resolve the issue.
If it is a neutral earth fault of high resistance then individual Insulation Resistance
testing of the circuits on the main board should highlight the potential problem, though it would also be critical that the earth was still connected to the earthing system to check for faults to an unexpected earthed part.
The rest of the advice already given above stands.
I would be heading for the NE fault area as a cause based on what you have described.
However only personal inspection and testing would be able to identify it accurately and it may well take a long time. An electrician could also possibly suggest some narrowing down methods if the fault is not clear cut.