I'm not even sure if I can properly explain this one. When the shower is switched on the RCD (1) on the other side of the board trips. The shower continues to work fine and when they come out they reset the RCD until the next person needs a shower.

When the hoover is switched on and plugged into the ring on RCD (1) side of the board the RCD (1) trips, but when the hoover is plugged into the ring on RCD (2) it is fine and works. Apparently the same thing happens with the kettle, sometimes. Other appliances are fine.

They did have a fire about five years ago and the place was partially rewired. A split board was put in about 2 years ago

IR tests are fine.
Neutrals are all correct.
Ring mains are not crossed.
 
As an aside, I had an RCD trip some times on a circuit with a freezer on it when I used a DIY tool or lawnmower in the RCD socket. The trip probably caused by earth leakage current from the freezer which is only operational when the freezer is actively cooling. I removed the RCD and used an extension cable with an RCD and there was not any tripping.

so some RCDs are more sensitive even though they have the same spec.
 
Could also be a poor neutral connection on the supply side. Have you ramp tested the RCDs?
 
Mystery solved. An extension cable plugged into a garden shed socket leading out to the garden to feed a water pump in a pond. The extension cable (socket end) wrapped up in a poly bag, left outside in Scotland. Sometimes dry, mostly wet. Never trust customer's explanantion of what is going on in their house holds.
 
Rule of thumb for RCD faults that 'just started to happen' is rain, DIY or faulty appliance.
 
Mystery solved. An extension cable plugged into a garden shed socket leading out to the garden to feed a water pump in a pond. The extension cable (socket end) wrapped up in a poly bag, left outside in Scotland. Sometimes dry, mostly wet. Never trust customer's explanantion of what is going on in their house holds.
Thanks for the update - very helpful!
 

Reply to RCD tripping on split board, strange one in the UK Electrical Forum area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
385
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
966
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
1K

Similar threads

Seen this where T&E has been fixed with a flat bend of too tight a radius.
2 3
Replies
35
Views
1K
My guess is an earth to N fault in the damaged light fitting. This will become a problem when other devices draw large currents.
Replies
2
Views
352

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top