Engineer54
quick question as well re RCDs, testing a village hall with 30ma up front of everthing rcd trips on 1/2 test With message TRP on the tester fine at x1 28 ms, same as 1/2 on x5 trips with TRP message, checked the booklet with the tester says that message is leekage on the curcuit, but its the same for all 16 curcuits, TT system 194 oms RA sound like a faultly trip ? All insulation test are >500 .
You should be testing at the load terminals of the RCD with the circuit/load cables disconnected. You won't see any natural leakage then... What do you expect with 16 circuits being monitored??