quick question as well re RCDs, testing a village hall with 30ma up front of everthing rcd trips on 1/2 test With message TRP on the tester fine at x1 28 ms, same as 1/2 on x5 trips with TRP message, checked the booklet with the tester says that message is leekage on the curcuit, but its the same for all 16 curcuits, TT system 194 oms RA sound like a faultly trip ? All insulation test are >500 .


You should be testing at the load terminals of the RCD with the circuit/load cables disconnected. You won't see any natural leakage then... What do you expect with 16 circuits being monitored??
 
I would do a ramp test and see what value it is actually tripping at with everything disconnected, it could be that on a single up front RCD that you have too much (normal) leakage, which is pushing it over the edge at 1/2Idn, and of course as you know, it should not trip at 1/2Idn.
 
I would do a ramp test and see what value it is actually tripping at with everything disconnected, it could be that on a single up front RCD that you have too much (normal) leakage, which is pushing it over the edge at 1/2Idn, and of course as you know, it should not trip at 1/2Idn.

The ramp test came in at 18ms with all curcuits/loads which can effect readings off.
 
So your RCD is likely OK then, as it is over 15mA , which is @ 1/2 Idn, I usually get circa 20-24 mA or there abouts.

It looks like you may have to split the circuits up across more than one RCD due to (legitimate ?) accumulated leakage currents.
 
Last edited:
This is the major problem with up-front RCD devices that are in effect monitoring the whole installation, and will be seeing all the normal/natural leakages from those circuits. The same goes for these dual RCD 17th CU's especially on the larger 12 and up way CU's... Nothing but trouble, when trying to fault find nuisance tripping as well!!
 
It may be worth trying another less sensitive RCD first, as 18mA is a little on the sensitive side.

But I don't think this will cure your underlying problem of too many (16 ?) circuits with accumulated leakage on one RCD, and this I think will be a problem of unwanted nuisance tripping further down the line. This is not good practice to have that many circuits on one RCD either, if not a direct contravention of the regs (reg 314).

Edit: Cross posted with E54
 
Thanks for the input guys, i have a load of square d rcbo's left over from a job i did when i was on the books ( which i can offer at a knock down price ), so think i will put this down as a code 3 with a veiw of installing 1 board with seperate rccbos, given the situation and the fact the current boards are full with some curcuits doubled up i think is a fair assessment.
 
RCBO's are a dream when it comes to fault finding, i've only fit one dual board in the last 2 years and that was by way of an apology to compensate for my mate thumping a dirty great hole in the living room plaster while working on the other side in kitchen lol.
 
All RCBO CU's are and will always be the preferred set-up and should be considered essential on TT installations!! Dual RCD CU's are basically a compromise, based purely on cost!!
 

Reply to RCD tripping times, 0.4 or <200 etc..... in the Electrical Wiring, Theories and Regulations area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Hi everyone, If you are looking for reliable EV chargers, check out our top-rated selection at E2GO! ⚡ Please note that all EV Chargers and...
Replies
0
Views
185
  • Article
As the holiday season approaches, PCBWay is thrilled to announce their Christmas & New Year Promotions! Whether you’re an engineer or an...
Replies
0
Views
1K
  • Article
Bloody Hell! Wishing you a speedy recovery and hope (if) anyone else involved is ok. Ivan
    • Friendly
    • Like
Replies
13
Views
1K

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top