From Understanding RCD´s by John Ware:
Operation of an RCD can occur due to a downstream fault such as a crossed neutral on a split-load board, high protective current or an upstream effect such as mains-borne disturbances.
Faults existing upstream of the RCD
13. A loose connection upstream of the RCD such as at the main switch or at the busbar connections can cause the device to operate.
14. Mains-borne disturbances such as spikes, voltage surges and dips, a lightning strike and the operation of distribution network switchgear and protective devices combined with capacitance to earth within the installation can cause unwanted RCD operation. A filter may be of assistance.
15. Site machinery or plant and installed services can cause mainsborne interference. Motors such as lift motors, control gear for discharge lighting and transformer inrush currents can cause unwanted RCD operation. Although significant transients can arise within an installation they would normally only occur under fault conditions. They might, however, travel to other installations where they could cause unwanted tripping of an RCD.
16. Overhead lines. Unwanted tripping may occur more frequently in an installation supplied by overhead lines compared to one supplied by an underground concentric cable. An underground concentric cable is, by its very nature, a good attenuator of transient overvoltages. Spurious tripping may be avoided by installing a filter upstream of the RCD at the origin of the installation.
http://---------------/Publish/WireRegs/WiringMatters/Documents/Issue19/2006_19_summer_wiring_matters_understanding_rcds.pdf