can anyone explain how an upstream supply fault can make an rcd trip?....shakey maybe:confused:
 
An RCD protects by constantly monitoring the current flowing in the live and neutral wires supplying a circuit or an individual item of equipment. Normaly, the current flowing in the two wires is equal. When an earth leakage occurs due to a fault in the circuit or an accident with the equipment, an imbalance occurs and this is detected by the RCD, which has a sensing coil inside which automatically cuts off the power before injury or damage can result.​
 
I think a high Ze on a TT will do this but only if you do not have an RCD as your main isolator. If it is a TT you are using, a higher Ze is permitted but not any higher than 100 ohms (a suggested resistance by Code of Practice for Earthing) and the isolator should have a 100mA rating to compensate for this.
 
From Understanding RCD´s by John Ware:

Operation of an RCD can occur due to a downstream fault such as a crossed neutral on a split-load board, high protective current or an upstream effect such as mains-borne disturbances.

Faults existing upstream of the RCD

13. A loose connection upstream of the RCD such as at the main switch or at the busbar connections can cause the device to operate.

14. Mains-borne disturbances such as spikes, voltage surges and dips, a lightning strike and the operation of distribution network switchgear and protective devices combined with capacitance to earth within the installation can cause unwanted RCD operation. A filter may be of assistance.

15. Site machinery or plant and installed services can cause mainsborne interference. Motors such as lift motors, control gear for discharge lighting and transformer inrush currents can cause unwanted RCD operation. Although significant transients can arise within an installation they would normally only occur under fault conditions. They might, however, travel to other installations where they could cause unwanted tripping of an RCD.

16. Overhead lines. Unwanted tripping may occur more frequently in an installation supplied by overhead lines compared to one supplied by an underground concentric cable. An underground concentric cable is, by its very nature, a good attenuator of transient overvoltages. Spurious tripping may be avoided by installing a filter upstream of the RCD at the origin of the installation.


http://---------------/Publish/WireRegs/WiringMatters/Documents/Issue19/2006_19_summer_wiring_matters_understanding_rcds.pdf
 
Last edited by a moderator:
yeah thanks, that was what i was looking for, i wonder if large barriers on train crossing near house could cause this?...........luke upstream being before installation, main fuse back towards transformer....
 
as above onit. its the outlaws house couple hundred yards from a main line crossing which has overheads aswell. Ive not looked at it yet just phone conversations:( tried the usual leaving lighting mcb's off, you know what its like over the phone talking to someone with no knowledge of electrics. Next door seems to be tripping alot though aswell. They left lighting mcbs off in the night to find the intruder batt went flat!no markings on mcb's!!
 
being the end users everything's up stream right up to the power station, therefore everything else is down stream from there...ye olde water analogy
 
Last edited by a moderator:
which way is upstream and down stream in the supply chain

cheers


Just to back up grey´s post:

Imagine an RCD was installed to the side of a current CU/DB (due to space constraints in the CU or the need to protect a new installed circuit to the 17th ect etc...) THEN UPSTREAM would be the cable taken from the CU, the CU to the meter etc etc...

Downstream would be the cable from the RCD for the circuit, the socket outlet (for example).

Think of it as a river - the source from the hill, downstream to the river, river to streams etc etc...
 

Reply to rcd in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
271
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
766
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
774

Similar threads

  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
682
If the main DB RCBO is there to provide additional protection (as it most probably is), then no, as S type RCDs are not suitable for providing...
Replies
1
Views
1K
loz2754
L

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top