Bazspark

When visiting relatives house she mentioned RCD was tripping sometimes and would i take a look. MEM split board and had no tools so i got on chair pressed trip button and no trip, told her trip was probably faulty and would replace. Returned another day with few tools in car and replaced trip. pressed test buton and still no trip so i put rcd tester on it and all fine, checked polarity with independant earth and all fine, house is TT system and trip is 30mA feeding shower, garage and sockets. also checked house earth spike and it was fine also. didnt have a lot of time to investigate further as it was also family visit but find it hard to believe that 2 trips had faulty trip button and when i simulated trip with bypass between neutral and earth trip functioned. anyone got any thoughts:confused::confused:
 
Just popped home for a cuppa, anyway sounds like your only problem is with functional testing of the RCD all else is ok. (Is that right)

If so I would follow the advice of previous posts regarding changing the RCD again. As said, its not immpossible for the new unit to be faulty.

Remember the test button generates an inbalance through the coil using a line resistor, that generates an eddie current in the relays secondary winding and the generated voltage differance operates the relay, with this in mind have you checked the mains voltage under load ? Also dont forget to check your tripping times on both ends of the waveform ie 0 degrees and 180.

It doesn't sound like a low neutral to earth resistance otherwise the rcd would be nuisance tripping, or crossed neutrals at the neutral bar. That would cause tripping the moment the offending circuits were energised.
Hope this info helps
 
I am going to change the trip again, thanks for input every one, I think my problem is myself refusing to believe two trips could be faulty and was hoping someone could give me a easy answer to save me having to change again. Will keep you all posted:)
 
How long has the fault been there ? did they have any work done just before it started or got a new bit of equip ? might be worth a check. All you can do is do tests/checks if all ok as said prob a faulty rcd although does sound strange that one.
Regards
Kung.
 
Does the MEM have a Functional earth cable?
The test button is usually a mechanical operation and shorts out as you described earlier. Could be faulty.
Yes the MEM trip had a functional earth cable which was properly connected to earth busbar and I have had some problems before with MEM trips which was why I thought it was the problem. The new trip I installed was a Hager and they have never given me any problems. Have not had a chance to revisit house yet but apparently New trip is not given nuisense tripping since but test button still not working. No new equipment in house and problem started about 3 months ago
 
Last edited by a moderator:

Reply to Rcd in the Australia area at ElectriciansForums.net

News and Offers from Sponsors

  • Article
Join us at electronica 2024 in Munich! Since 1964, electronica has been the premier event for technology enthusiasts and industry professionals...
    • Like
Replies
0
Views
288
  • Sticky
  • Article
Good to know thanks, one can never have enough places to source parts from!
Replies
4
Views
790
  • Article
OFFICIAL SPONSORS These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then...
Replies
0
Views
811

Similar threads

L
  • Question
My Understanding is the 6 Months interval is IET Guidance and this wording is incorporated onto the label which is a requirement in 514.12.2 where...
Replies
9
Views
654
  • Question
I would add though that a typical good TT rod of 100 ohms only needs 3V to have 30mA flowing and so trip an RCD, you might find that sort of N-E...
Replies
8
Views
685

OFFICIAL SPONSORS

Electrical Goods - Electrical Tools - Brand Names Electrician Courses Green Electrical Goods PCB Way Electrical Goods - Electrical Tools - Brand Names Pushfit Wire Connectors Electric Underfloor Heating Electrician Courses
These Official Forum Sponsors May Provide Discounts to Regular Forum Members - If you would like to sponsor us then CLICK HERE and post a thread with who you are, and we'll send you some stats etc

YOUR Unread Posts

This website was designed, optimised and is hosted by untold.media Operating under the name Untold Media since 2001.
Back
Top